My plan (please correct me if wrong)
From inside home running SER AL 2-2-2-4 off of a 90 AMP breaker down stud cavity wall into an exterior junction box
Inside the junction box, using Polaris connectors converting to individual wire(s)
Three 2 AWG AL XHHW-2 (two hot, one nuetral)
One 4 AWG AL XHHW-2 for ground.
Not sure if Home Depot sells the XHHW-2 or just XHHW bare wire, if not I can order the XHHW-2 from wireandcableyourway dot com
Individual wire will be run inside 2" pvc conduit (minimum 18" to top of conduit) - probably a total run approx max 75'
Run conduit /wires into another junction box mounted on outside of exterior outbuilding
Inside that junction box, use Polaris connectors to convert back to SER AL 2-2-2-4.
Run SER 2-2-2-4 up stud cavity into subpanel.
Install 2 8- ground rods (believe they are 5/8" copper) - min' 6' apart, connect ground wire (#6 copper) into subpanel
Afterwards, open a 6 pack of busch
Thanks
From inside home running SER AL 2-2-2-4 off of a 90 AMP breaker down stud cavity wall into an exterior junction box
Inside the junction box, using Polaris connectors converting to individual wire(s)
Three 2 AWG AL XHHW-2 (two hot, one nuetral)
One 4 AWG AL XHHW-2 for ground.
Not sure if Home Depot sells the XHHW-2 or just XHHW bare wire, if not I can order the XHHW-2 from wireandcableyourway dot com
Individual wire will be run inside 2" pvc conduit (minimum 18" to top of conduit) - probably a total run approx max 75'
Run conduit /wires into another junction box mounted on outside of exterior outbuilding
Inside that junction box, use Polaris connectors to convert back to SER AL 2-2-2-4.
Run SER 2-2-2-4 up stud cavity into subpanel.
Install 2 8- ground rods (believe they are 5/8" copper) - min' 6' apart, connect ground wire (#6 copper) into subpanel
Afterwards, open a 6 pack of busch

Thanks