Subpanel wiring help

jrz126

Member
Joined
Oct 12, 2010
Messages
6
Just moved into a house with 2.5 car detached. Previous owner only ran a 30a 120v circuit. Trying to upgrade to 240v 60A panel for the welder.

Main panel is on opposite side of the house, 50' run inside, 20' run outside, and 5' inside detached garage. So I figured 100' of 6/3 UF would be plenty. And I wouldnt have to mess with conduit, etc.

Turns out I'm 10' short. What should I do?
Thinking splice it?
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,034
Location
Richmond, VA
Install an accessible box and splice in the box.

Either a box on the house/in the house, or new wire.

Where are the dimensions off? Any chance of changing the run to find 10'.

If you put the box inside, you can switch to nm-b. If you do it outside, I would run conduit anyway for that short distance. Then you can use thhn
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,034
Location
Richmond, VA
Miss calculated and got bit.. Live and Learn.

Buy new wire.

If the wire is already run, that is easier said than done. Why undo all of it if it is a relatively simple junction, plus 6/3 uf isn't cheap
 
Last edited:

510ebl

Well-known member
Joined
Jan 20, 2015
Messages
518
Location
Southern New Jersey
Are you certain that you received the 100ft that you purchased? It seems unlikely that you would be 35 ft off on a 75 ft measurement.
 