Hey Guy's,
I'm at a loss here, just don't know waht to do. I'm pretty much done running my wires in the garage and this is what I have. 100 AMP subpanel
2 - 15 amp circuits for recepticals
1 - 15 amp circuit for the lights
1 - 15 amp circuit for the drop light, garage door opener and outdoor sensor light
1 - 20 amp circuit for recepts around the work area
1 - 40 amps going to the (attached Shed) which has lights a baseboard heater, some recepts and the compressor(5HP 1 stage 3 cyl pump FLA 21)
1 - 60 Amp for the welders/Plasma (I work alone so would never be using 2 or 3 at the same time)
1 - 30 Amp for the heater for in floor heat
Now as per many discussions on the electrical, I should be running 50 Amp breaker and min 8 gauge wire for the compressor. (21 x 175%= 36.75) (21 x 250%=52.5)
now the 8 gauge I alread had so was using it anyway no biggie, what my problem is the shed is attached to the garage, I will be using it to store parts and stuff in general as well as having the compressor in there (hence the baseboard heater to keep the room above freezing). The thing is, the shed has a subpanel of it's own(previous owner was running 40 Amps to it). so if I run leave it and run the 40 Amps to the shed subpanel from there would it be just too much to run the compressor off a 30 Amp breaker, the heater on 20 Amps and occasionally turn the lights on (4 - 4' bulb florescents 46 watts each)?
Or should I jsut say screw it and wire the compressor direct off the 8 gauge and a 50 Amp breaker, then buy some 10 gauge to run to the panel off a 30 Amp breaker? I'd have to purchase the 30 amp main breaker for the square D in the shed, and the 10 gauge wire, so I'm lookin around 120$. the other method, I have what I need.
Also, I'm going to have a PC with internet(for those quick search needs) and a TV with one of those cheap DVD's (20$ jobbies). before I put the drywall up, I'm thinking hard to put up 1 more 15 Amp circuit just for those, to leave my working circuits seperate. I could also theoretically use this last circuit for those hidden items that draw power(batterie chargers, possible bar fridge, etc..)
In my mind I know what I should do but having a hard time making that final decision, what do you think?
and thanks
I'm at a loss here, just don't know waht to do. I'm pretty much done running my wires in the garage and this is what I have. 100 AMP subpanel
2 - 15 amp circuits for recepticals
1 - 15 amp circuit for the lights
1 - 15 amp circuit for the drop light, garage door opener and outdoor sensor light
1 - 20 amp circuit for recepts around the work area
1 - 40 amps going to the (attached Shed) which has lights a baseboard heater, some recepts and the compressor(5HP 1 stage 3 cyl pump FLA 21)
1 - 60 Amp for the welders/Plasma (I work alone so would never be using 2 or 3 at the same time)
1 - 30 Amp for the heater for in floor heat
Now as per many discussions on the electrical, I should be running 50 Amp breaker and min 8 gauge wire for the compressor. (21 x 175%= 36.75) (21 x 250%=52.5)
now the 8 gauge I alread had so was using it anyway no biggie, what my problem is the shed is attached to the garage, I will be using it to store parts and stuff in general as well as having the compressor in there (hence the baseboard heater to keep the room above freezing). The thing is, the shed has a subpanel of it's own(previous owner was running 40 Amps to it). so if I run leave it and run the 40 Amps to the shed subpanel from there would it be just too much to run the compressor off a 30 Amp breaker, the heater on 20 Amps and occasionally turn the lights on (4 - 4' bulb florescents 46 watts each)?
Or should I jsut say screw it and wire the compressor direct off the 8 gauge and a 50 Amp breaker, then buy some 10 gauge to run to the panel off a 30 Amp breaker? I'd have to purchase the 30 amp main breaker for the square D in the shed, and the 10 gauge wire, so I'm lookin around 120$. the other method, I have what I need.
Also, I'm going to have a PC with internet(for those quick search needs) and a TV with one of those cheap DVD's (20$ jobbies). before I put the drywall up, I'm thinking hard to put up 1 more 15 Amp circuit just for those, to leave my working circuits seperate. I could also theoretically use this last circuit for those hidden items that draw power(batterie chargers, possible bar fridge, etc..)
In my mind I know what I should do but having a hard time making that final decision, what do you think?
and thanks