Support column as electrical raceway?

Slowbuilder

Well-known member
Joined
Mar 14, 2016
Messages
267
Location
Chandler, AZ
Hey Sparkies!!

I have an outdoor shade structure that sits on a concrete slab and has a frame of 3" galvanized pipe with a corrugated tin roof. The pipes are structural, open at the ends, and bolted together to form the frame. I have power on one side of the structure, and I would like to hang some outdoor lights on the opposite side of it.

Can I use the horizontal 3" galvanized pipe that is under the roof as a raceway to run THHN from one side to the other, or do I need to put conduit (EMT, likely) inside (or outside for that matter) the pipe?

It's not a huge deal, as the structure is only about 19' wide.

Here's a photo of a typical corner "joint" of the structure.
 

Attachments

  • Shade canopy detail.jpg
    Shade canopy detail.jpg
    30.9 KB · Views: 51
To avoid these ads, REGISTER NOW!

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,921
The pipe is not rated as a raceway. Run conduit, or use low voltage stuff with wire in the pipe.
 

southalabama

Well-known member
Joined
Jan 10, 2011
Messages
5,547
Location
Brewton AL
Standard galvanized water pipes have rough interior seams or burrs that can strip wire insulation, and they lack certification under the National Electrical Code (NEC).

Use the proper conduit.
 

Codyboy

Well-known member
Joined
Jan 31, 2019
Messages
1,747
Location
S.E. TEXAS
That doesn't look like 3", but whatever.
Are you sure its not actually "conduit" instead of pipe?

Either way I would do it but use a bushing on the ends.
However it's going to look dumb and will be unprotected if the wire will be exposed from where it exits the one conduit and going into the other conduit.
 

willf650

Well-known member
Joined
Mar 10, 2010
Messages
981
As others have mentioned your only option that would be code compliant would be UF.

MC is not rated for wet locations and your pictures appear that would be the case.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,719
Location
Long Island
As others have mentioned your only option that would be code compliant would be UF.

MC is not rated for wet locations and your pictures appear that would be the case.
You could pipe with PVC (better outside) or EMT or rigid, flex pipe with LFNC or LFMC (preferred). If you go with UF, you need bushings on the sharp metal ends.

That "pipe" looks like the stuff used for fence posts. If so, and if using UF, I'd get a nice looking aluminum cap and drill it for a plastic romex bushing type clamp.

edit: and then I'm forgetting tray cable - duh. On second thought, that may be the best bet. Mini-split power/control cable is TC rated. Sunlight and water resistant and way more damage resistant than UF.
 
Last edited:
To avoid these ads, REGISTER NOW!

willf650

Well-known member
Joined
Mar 10, 2010
Messages
981
They make it in pvc jacketed as well as rated fittings.
Yes but it's not readily available to a home consumer, at least around me. It's only sold on large spools at my local supply house. You may be able to buy a "cut" but I've never tried.

I only said MC because someone mentioned "metal flex" and assumed that may be what they were talking about.

I personally would run emt as well but UF fished in the pipes may be the cheapest and quickest solution.
 
OP
S

Slowbuilder

Well-known member
Joined
Mar 14, 2016
Messages
267
Location
Chandler, AZ
Thanks for all your input. I'll likely run EMT and attach it to the outside of the "pipe". Why is ENT "better" outside? Here in AZ, the severe sunshine attacks PVC with a vengeance. It would have to be wrapped, especially where it's out from under the tin on the roof.
 

willf650

Well-known member
Joined
Mar 10, 2010
Messages
981
PVC is for underground to me and that's about it.

I know my opinion will be met with opposition.

It ages, breaks and expands like a champ.

He maybe talking Smurf tube but I've never seen it installed outside. Thats what I think of when someone says ENT. Never heard anyone call PVC conduit ENT except on this forum I guess.
 
Last edited:

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,278
Location
Minneapolis
Nonmetallic won't rust, but it can sag in very hot conditions. The usual solution for that is more closely spacing the conduit clamps or supports. Painting it can help protect it from UV from the sun, but then it becomes a maintenance issue since it will need to be repainted every so often.
 

willf650

Well-known member
Joined
Mar 10, 2010
Messages
981
Yes. Is PVC conduit just that? No other designation?

And I did think of it as inside the 3" structural pipe, solving the UV issue. Also did not notice it was in AZ until later, which affects it a lot. EMT outside here would be rusted pretty quickly.
RNC -but its antiquated and Rigid PVC is specified in the code book by name at this point.