c.snyder
Member
Hello everyone. Hopefully this isn't as serious as i think it is but we'll find out. For a little background, i purchased this garage three years ago and just this year i've been getting around to remodeling it. The front part is typical 2x4 frame on slab and the back addition i'm dealing with is a post frame style building. The concern i have is with the rafters themselves. When i initially inspected them earilier this spring, i discovered that the builder had used two 2x6 boards to make up the span for each rafter tie on the bottom. His flaw was that he tried to join the two together in the middle with a small 2x4 and only a couple nails. Obviously the 2x4 split easily from the tension pulling on each 2x6.
To fix this issue i purchased enough 2x6's to fill in every other rafter he skipped so that they are now 24" OC and also i used a short 2x6 in the middle with four 1/2" hex bolts joining them together, two in each side. Each rafter tie is connected to the rafter at the wall with a single 1/2" hex bolt. This obviously isn't an issue now and the bolts were probably overkill. Yeah there's a slight sag in the ridge from the small amount the walls did push out but looking at the wall from the outside you can't notice any outward lean. If anything i believe the walls were leaning slightly inward to begin with since they are nearly level now. Given this i didn't try to mess with the rafters i just wanted to arrest this thrust issue so it didn't go any further.
Now the issue im dealing with is the span of the rafters themselves. Per my calculation, #2 SPF 2x6 rafters installed to handle roughly 10 psf of dead load and 20 psf of snow load should not span more than about ten feet to ridge. These 2x6's span 14 1/2 feet. Obviously these need support and i can tell they are beginning to sag. I've researched purlins and knee walls but from what i can gather these need to be installed in such a way they bear on an interior bearing wall. I understand you can't bring your braces down on the rafter ties as this will just sag the tie. My question is, what options do i have here to brace the rafters? There are no interior walls to brace to and the only other support i have under the rafter ties is at the mid span of the room. This is a double 2x10 beam that runs perpendicular to the ties and will be supported at each end by a 6x6 post down to footing. I'd like to figure something out before winter hits and there is a significant snow load on the roof. I added some pictures but i can get more if needed.
To fix this issue i purchased enough 2x6's to fill in every other rafter he skipped so that they are now 24" OC and also i used a short 2x6 in the middle with four 1/2" hex bolts joining them together, two in each side. Each rafter tie is connected to the rafter at the wall with a single 1/2" hex bolt. This obviously isn't an issue now and the bolts were probably overkill. Yeah there's a slight sag in the ridge from the small amount the walls did push out but looking at the wall from the outside you can't notice any outward lean. If anything i believe the walls were leaning slightly inward to begin with since they are nearly level now. Given this i didn't try to mess with the rafters i just wanted to arrest this thrust issue so it didn't go any further.
Now the issue im dealing with is the span of the rafters themselves. Per my calculation, #2 SPF 2x6 rafters installed to handle roughly 10 psf of dead load and 20 psf of snow load should not span more than about ten feet to ridge. These 2x6's span 14 1/2 feet. Obviously these need support and i can tell they are beginning to sag. I've researched purlins and knee walls but from what i can gather these need to be installed in such a way they bear on an interior bearing wall. I understand you can't bring your braces down on the rafter ties as this will just sag the tie. My question is, what options do i have here to brace the rafters? There are no interior walls to brace to and the only other support i have under the rafter ties is at the mid span of the room. This is a double 2x10 beam that runs perpendicular to the ties and will be supported at each end by a 6x6 post down to footing. I'd like to figure something out before winter hits and there is a significant snow load on the roof. I added some pictures but i can get more if needed.
Last edited: