Supporting wire in the attic over joists

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
My panel is at one end of the shop and I need to run circuits up into the attic, down the attic and then turn 90 degrees run across the attic and drop down the walls to the outlets, disconnects, or whatever. I will have 12 gauge, 10 gauge, and maybe some 8 gauge romex cables to run in the attic for these ciruits. There will be long runs that are parallel to the ceiling joists which are 2 feet apart. Every four feet I have a flat 2x4 that runs perpendicular to the long wire runs.

My question, since I can't nail all the circuits to one joist, how often must a cable be supported when running in free air parallel to the joists. I know I can go two feet but how about 4? There will be a ceiling at some point and this will be inspected.
 

Attachments

  • IMAG0548.jpg
    IMAG0548.jpg
    95.6 KB · Views: 89
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Support/staple needs to be within every 4 1/2 feet and within 12" of every outlet or Jbox. Also any cable run across joist within 6' of an attic access hole must be run along a running board.
 
Last edited:

LX-Markham

Well-known member
Joined
Apr 27, 2013
Messages
2,930
Location
Markham, Ont.
LOL that's only the second time I've heard that term ^^^.
Two weeks ago my contractor called them rat runs.

I guess only engineers call them "joist bridging"
 

tylernt

Well-known member
Joined
Jan 24, 2013
Messages
182
Location
Idaho, US
Support/staple needs to be within every 4 1/2 feet
Do they still need staples even beyond 6' from an attic scuttle hole? Because every attic I've ever seen, has Romex everywhere with no staples whatsoever... including one that I know was re-wired by a licensed sparky and inspected by the AHJ.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
All I can say is the NEC says the cable is to be supported/secured at intervals not to exceed 4 1/2'. The only exception is cable that is protected within a raceway is not required to be secured within the raceway.
 
To avoid these ads, REGISTER NOW!

tylernt

Well-known member
Joined
Jan 24, 2013
Messages
182
Location
Idaho, US
All I can say is the NEC says the cable is to be supported/secured at intervals not to exceed 4 1/2'. The only exception is cable that is protected within a raceway is not required to be secured within the raceway.

I guess running perpendicular to ceiling joists, the cable is "supported" every 16" or 24" O.C. Running parallel with the joists, I suppose the insulation or ceiling drywall underneath might count as support.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Nope. The support has to be done with staples, cable ties, straps, hangers, etc.

I guess running perpendicular to ceiling joists, the cable is "supported" every 16" or 24" O.C. Running parallel with the joists, I suppose the insulation or ceiling drywall underneath might count as support.
 

tylernt

Well-known member
Joined
Jan 24, 2013
Messages
182
Location
Idaho, US
Nope. The support has to be done with staples, cable ties, straps, hangers, etc.
Guess the inspectors in my area just have a really relaxed attitude towards life. :)

(Don't worry, when I added a circuit, I stapled... it's the only cable up there that's stapled, but I still did it.)
 
OP
H

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
LOL that's only the second time I've heard that term ^^^.
Two weeks ago my contractor called them rat runs.

I guess only engineers call them "joist bridging"

As an engineer myself, I learned early on to use the common lingo for such things. It's the only way you can expect to get knowledgable responses from people that actually do this stuff.
 

2Big2Ride

Well-known member
Joined
Oct 24, 2010
Messages
258
Location
d/FW, Texas - more FW than D
All I can say is the NEC says the cable is to be supported/secured at intervals not to exceed 4 1/2'. The only exception is cable that is protected within a raceway is not required to be secured within the raceway.
Our old house in Vancouver, Washington that was built in 1992 was done as discribed, our current house in Texas that was built 1999 isn't even close. I think they used at most two staples per run and the attic looks a bowl of spaghetti.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Our old house in Vancouver, Washington that was built in 1992 was done as discribed, our current house in Texas that was built 1999 isn't even close. I think they used at most two staples per run and the attic looks a bowl of spaghetti.

SOP for years in houses. I've never seen a staple in a attic. None in ours that's for sure. In the shop, I used the bottom of the rafter bracing and some 1x to make cable trays.

Power13.jpg
 