MTW: Understand how having a good ground is usually best, but here in Ontario Canada we can only have the separate building with a ground rod or sent back to the main building:
The device I'm wondering about is this one:
http://www.amazon.com/dp/B0052MG5K0/?tag=atomicindus08-20
Re-reading the instructions it says it can only be used in a panel with a grounded neutral, which I'm assuming I have since the neutral goes back to the main panel and then ground.
I don't work in Canada, and therefore don't know the code there or have a copy, but the rule you posted appears very similar to the NEC.
Quote:
10-208 Grounding connections for two or more buildings or structures supplied from a single service
Where two or more buildings or structures are supplied from a single service,
(a) the grounded circuit conductor
(neutral) at
each of the buildings or structures
shall be connected to a
grounding electrode and
bonded to the non-current-carrying
metal parts of the electrical equipment; or
(b) except for buildings housing livestock, the non-current-carrying metal parts of the electrical equipment in or on the building or structure shall be permitted to be bonded to ground by a bonding conductor run with the feeder or branch circuit conductors.
The way I read this is you
must have an electrode at each structure, and nowhere does it say that you are limited to one. Same basic rule as NEC. You might want to check with a different contractor than the one you are using for their interpretation. Earthing electrodes are just like the surge suppressors, the more the merrier, lower earth resistance (impedance) = greater dissipation capability.
As to your suppressor in the link you provided that only has a neutral connection. I took a look at the specs for the device
w3.usa.siemens.com/.../us/en/.../sf-11-sect-01-044-046.pdf
Catalog NumberQSA1515SPD QSA2020SPD
Amperage15 or 20 Amp
Number of Poles(2) 1-Pole Circuit Breakers
Initial Clamping Level 240 Volts
Transient Energy Rating 360 Joules line-to-neutral 7
20 Joules line-to-line
Transient Suppression500 volts peak, line-to-neutral
Voltage Rating1000 volts peak, line-to-line
Peak Current Rating (impulse)40,000 amperes
Discharge Voltage Characteristic@ 1,500A, 600 volts@ 5,000A, 800 volts(both line-to-neutral)
Discharge Current Withstand Rating 10,000 amperes line-to-neutral
Circuit Breaker Interrupting Rating 10,000A, 120/240V ACListings/Certifications UL, CSA Meets UL 1449 3rd Edition
When using this MOV suppression breaker in a sub-panel in a separate structure, it is a good example of why you want an additional earth electrode at the separate structure.
Consider this, when this device does it's intended function, it shunts the excess energy to the neutral buss. In your sub-panel the neutral buss is isolated. Therefore any surge it shunts will have to travel back to the main panel neutral buss before it can connect and discharge to the earth or transformer. Forcing it back through your feeder neutral could possibly affect devices connected to the main panel neutral. In my opinion a better strategy would be to have a quality earth electrode at the subpanel (remote structure) and a MOV suppressor that could shunt the excess energy to the local earth electrode. This would also save wear and tear on the MOV's at the main panel and point of use units in the main structure.
By the way the PDF link above also list suppression devices for the other services that were mentioned earlier, cable, phone, data. Without connecting the other systems to the earth, you will still be vulnerable to surges from the other systems.
MTW Ω