fnieto
Well-known member
Today I got her wired and plumbed. Fired up a Arocool IUP701 11,700 cfm swamp cooler. It's a two wet section commercial unit with 8" pads that should cool a 3200 sf shop. (40'X80') space. We calculated the ductwork and ordered up the spiral oval sections but still need to hang it. Today we erected the updraft ductwork but had a difficult time getting the amperage set right. The belt was very loose in order to get the amps set right. We ran 230 vac for this 2 hp motor which should pull 10.5-11.3 amp load when adjusted properly. The pulley is adjustable as well as the motor mounts, but when the belt is snug and not slipping at start up its pulling over 20 amps causing the circuit breaker to pop. We tried adjusting the pulley to bring down the amps but the temp on the pully itself got very high (around 250 degrees with temp gun) and belt tension was real loose. The pulley is turned out about five turns (from all the way in) to get the amps right but caused the pulley to get hot as well as belt to be very loose. What am I doing wrong?
I forgot to mention, I installed all the grill/defusers prior to final adjustments and readings.