MattGarage
Well-known member
Hi all, planning 240v outlet for a swim spa. The specs are as follows:
* Manufacturer calls for 50A service (want to do 60a)
* Calls for 6/3 wire with ground if distance under 40 feet
* My distance is about 105 feet (maybe add 10 ft to be conservative)
* Online wire calculators such as this appear to show that the 6 AWG would suffice with voltage drop < 3%. What should it be?
* All wiring would be outside/buried in conduit
I'm racking my brain on whether 4/3 would be appropriate or if I can rest easy that 6/3 would do the job.
Thank you!