Switch leg question about the code

Coyote556

Well-known member
Joined
May 6, 2013
Messages
108
Location
The Show-Me State
If I am running emt conduit to a two pole switch some distance from the light, can I just run the two black switching wires and a ground in that emt run or do I need to run the neutral also? If I have to run the neutral also, do I just loop it in the box?

I know I technically dont have to run a ground because I could use the emt, but I am running a ground to everything else.

Thanks
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Two black switch wires is not enough for a "two pole" switch. Sounds like a regular light switch to me. Neutral. Yes code requires a neutral in the switch box even if you do not use it. Just cap it off.
 

APEowner

Well-known member
Joined
Oct 2, 2009
Messages
4,164
Location
Sunny, New Mexico
Yes code requires a neutral in the switch box even if you do not use it. Just cap it off.

Really!? I did not know that and I'm certain I've seen it done without the neutral many times (not that's any gaurentee that it's correct)

Can you elaborate on that? What is the reason for that?

Is that just if you're running individual wires in conduit?

Does that mean that If I'm doing a Romex run to a switch that I need to use 3 wire plus ground even though one wire isn't doing anything?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Really!? I did not know that and I'm certain I've seen it done without the neutral many times (not that's any gaurentee that it's correct)

Can you elaborate on that? What is the reason for that?

Is that just if you're running individual wires in conduit?

Does that mean that If I'm doing a Romex run to a switch that I need to use 3 wire plus ground even though one wire isn't doing anything?

The reason the NEC now requires a neutral in the switch box is because so many smart switches now require power to operate. Actually the neutral can be left out if it can be easily added without removing finished wall materials. Look up 2014 NEC 404.2. I believe it started with the 2011 NEC.

*
 
Last edited:

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
The Code says that conduit such as EMT and flex are exempt from the "neutral at the switch" rule because another wire could be installed in the conduit at a later time.

It only applies to cable system like NM, AC, MC and the like
 
Last edited:
OP
C

Coyote556

Well-known member
Joined
May 6, 2013
Messages
108
Location
The Show-Me State
So for a standard light switch I just need the two blacks and the ground? For three way I need two blacks, traveler, and ground? No neutral to box on either is OK? Thanks
 
To avoid these ads, REGISTER NOW!

toplessHO

Well-known member
Joined
Oct 20, 2014
Messages
14,011
Location
central florida
everyone makes 3 way switches so complicated when its not
hot on one switch
switch leg on the other
two wires between (travelers)
add grounds and neutrals at each box if required
the only booboo you can do is reverse the travelers
 
Last edited:

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Only thing I can say is that once you get it working, you will suddenly discover that you want to install some fancy motion sensor/timer/whatever switch and sensor and will be wishing for the neutral, only to discover that you get your fish tape hung up in the conduit with the other wires and have to pull the whole shebang out to pull the neutral back in, kicking yourself the whole time..........

Charles
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
everyone makes 3 way switches so complicated when its not
hot on one switch
switch leg on the other
two wires between (travelers)
add grounds and neutrals at each box if required
the only booboo you can do is reverse the travelers

You're assuming that the bone heads...er...professional that put it in didn't use all black wire. And ran a couple of other circuits though the boxes just for confusion.
 

APEowner

Well-known member
Joined
Oct 2, 2009
Messages
4,164
Location
Sunny, New Mexico
The reason the NEC now requires a neutral in the switch box is because so many smart switches now require power to operate. Actually the neutral can be left out if it can be easily added without removing finished wall materials. Look up 2014 NEC 404.2. I believe it started with the 2011 NEC.

Well, how about that, I learned something! Thank you. And, now that you mention it I have that exact issue in my house. If that requirement had been in place when my house was built I could have installed that fancy light timer on the yard lights that my wife wanted.
 