It doesn’t quite work that way. You’re getting about 16,800 Lumens out of each fixture. Using an estimated 13ft from floor to fixture face and surface reflectance of: 50% Ceiling, 60% Wall, 20% Floor, you’ll achieve an average of 68 lumens at the floor. It’ll be much higher directly beneath the fixture and lower between them.
You’re using a high bay fixture for a standard lighting application, thus you get glare. Looking at the 2 fixtures to the left and right of the garage door, you can make out the beam spread pattern on the wall. In a properly lit space it should not be this defined.
Your average 68 lumens would be fine if it was evenly distributed. It could be worse, but it could also be better. As discussed in
this thread using the Cooper/Metalux 4 lamp F32T8
HBL-432-N-UNV-EB81/PLUS fixture.
Qty.20
Garage: X,Y = 40 x 60
Fixture Arrangement: X,Y = 4 x 5 (fixtures parallel with 60ft)
Spacing: X,Y = 10 x 12ft (fixture center to center)
Lumen Yield = 96 lumens