t8 fixture power usage?

slakwhere

Active member
Joined
Sep 19, 2011
Messages
42
so the new garage i'm buying only has 2 60 watt bulbs in the whole thing :willy_nil

i need to add some lighting, and it looks like T8 is the way to go... but i'm curious what a standard 32w bulb pulls for amps. is the standard equation of Watts/volts = Amps? or do these things peak/burst/pulse higher?

my plan is to go 36 bulbs (4 per fixture, 9 fixtures) on 2 separate switches, but i'm wondering what kind of load this will generate so i can calculate the wire gauge accurately. current plan is 16 gauge wire so each circuit can handle 20 amps.

5 fixtures X 4 bulbs X 32 watts = 640 watts / 120v = 5.3 amps?
9 fixtures X 4 bulbs X 32 watts = 1152 watts / 120v = 9.6 amps?
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
that would be 12ga wire, not 16.

on fluorescent fixtures ignore the bulb wattage -you have to look at the current draw printed on the ballast.
 
To avoid these ads, REGISTER NOW!
OP
S

slakwhere

Active member
Joined
Sep 19, 2011
Messages
42
that would be 12ga wire, not 16.

on fluorescent fixtures ignore the bulb wattage -you have to look at the current draw printed on the ballast.

mrb guess i have to go back to home depot and see what the ballasts say they draw :shocking: :thumbup:
 

StaggeringGoat

Well-known member
Joined
Jul 1, 2011
Messages
758
Location
Oregon
You also have to calculate the ballast factor, some are less than 1, some are more than 1. That means they feed the bulbs more or less wattage. I have some 2-tube fixtures with Sylvania ballasts and they only draw 50 watts, even though there is 64 watts of tubes.
 
OP
S

slakwhere

Active member
Joined
Sep 19, 2011
Messages
42
with 12ga wire and 5 lights per circuit i should be WAY under what's expected... but i'll double check ballast #'s to be sure.
 
To avoid these ads, REGISTER NOW!