Taco relay wiring

Bangon61

Well-known member
Joined
Jul 29, 2020
Messages
88
Location
BC
Can't figure out why my taco relay isn't sending power to my pump. As you can see in pictures, I have 24 vac to r and w inside relay. Also have 24vac to r and com. On the lower connections I have 110v going to n and h. But no 110v to n and 4. Thermostat says calling for heat. What am I missing? Thanks in advance20230102_114445.jpg20230102_114445.jpg20230102_114445.jpg20230102_114445.jpg20230102_114445.jpg
 
To avoid these ads, REGISTER NOW!

chinboys

Well-known member
Joined
Jun 20, 2011
Messages
434
What is N (neutral?) to the ground?
What is H (L1) to the ground?
Before the call (relay goes active) for the pump to turn on?
Same questions for the above when the call for the pump to come on.

I am not sure if you also measured the relay's voltages correctly before the call signal or after the call signal was made from boiler and or thermostat.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,991
Location
Peace Valley,mo
Thermostat or end switch isn't calling.
Meter R to W 24vac not calling
Meter R to W 0 vac calling
Meter R to common. 24vac
Still not working check the fuses
Bad fuse across it 120vac
Good almost 0 vac probably 1 or 2 volts
 
To avoid these ads, REGISTER NOW!
OP
B

Bangon61

Well-known member
Joined
Jul 29, 2020
Messages
88
Location
BC
Sew. When I jump the wires on the stat, everything is groovy. Apparently honeywell support is in order.
 