tailing panel bonding

jdieter

Well-known member
Joined
Nov 17, 2007
Messages
320
Location
Northern Indiana
When I wired a couple outbuilding from the main service entrance I ran 4 conductors in pvc. The 4th conductor was to bond the tubs with a floating neutral bar unlike the main service entrance panel which has the neutral bar bonded to the tub. At the time that was NEC code practice. Has that part of the code changed?
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,257
Location
Modesto, CA
When I wired a couple outbuilding from the main service entrance I ran 4 conductors in pvc. The 4th conductor was to bond the tubs with a floating neutral bar unlike the main service entrance panel which has the neutral bar bonded to the tub. At the time that was NEC code practice. Has that part of the code changed?

Prior to 2008, code allowed bonded neutral and 3-wire feed to a detached structure, as long as there was no parallel metallic pathways

in 2008, the code changed and thus no longer allowed that and it hasn't changed back since then.

If you go to this thread and read post #3, you will see all the info you need

https://www.garagejournal.com/forum/showthread.php?t=356460
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
When I wired a couple outbuilding from the main service entrance I ran 4 conductors in pvc. The 4th conductor was to bond the tubs with a floating neutral bar unlike the main service entrance panel which has the neutral bar bonded to the tub. At the time that was NEC code practice. Has that part of the code changed?

if you want to bring it up to current code, which would be a good idea, you just need to unbond it. should be as simple as moving your grounds over to a separate bar and removing the bonding screw from the existing neutral bar. Pics would help confirm that.
 
OP
J

jdieter

Well-known member
Joined
Nov 17, 2007
Messages
320
Location
Northern Indiana
wyliesdiesels - based on my original post, to bring my 1990's installation up to date, all I need is add code approved ground rod and associated conductor to bonding bar in the tail panel, correct?
I retired as an industrial electrician in 2007 and haven't looked at a code book since, by the way very nice visual on post #3?
 

AP514

Well-known member
Joined
Jan 23, 2014
Messages
768
Location
Pearland, Tx
+1 on the Sticky Thread and Post #3
(maybe a Mod can Delete that gubbers stuff that kind of side tracked part of it.)
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,257
Location
Modesto, CA
wyliesdiesels - based on my original post, to bring my 1990's installation up to date, all I need is add code approved ground rod and associated conductor to bonding bar in the tail panel, correct?
I retired as an industrial electrician in 2007 and haven't looked at a code book since, by the way very nice visual on post #3?

as long as the neutral bar is isolated, then yes you just need 2 ground rods.
 