I'm doing a bit of electrical work in a detached garage. Are tamper resistant outlets required in a detached?
406.12 Tamper-Resistant Receptacles.
All 15- and 20-ampere, 125- and 250-volt nonlocking-type receptacles in the areas specified in 406.12(1) through (7) shall be listed tamper resistant receptacles.
(1) Dwelling units in all areas specified in 210.52 and 550.13
(2) Guest rooms and guest suites of hotels and motels
(3) Child care facilities
(4) Preschools and elementary education facilities
(5) Business offices, corridors, waiting rooms and the like in clinics, medical and dental offices and outpatient facilities
(6) Subset of assembly occupancies described in 518.2 to include places of waiting transportation, gymnasiums, skating rinks, and auditoriums
(7) Dormitories
Informational Note: This requirement would include receptacles identified as 5-15, 5-20, 6-15, and 6-20 in ANSI/NEMA WD 6-2016, Wiring Devices — Dimensional Specifications.
Exception to (1), (2), (3), (4), (5), (6), and (7): Receptacles in the following locations shall not be required to be tamper resistant:
(1) Receptacles located more than 1.7 m (5 1∕2 ft) above the floor
(2) Receptacles that are part of a luminaire or appliance
(3) A single receptacle or a duplex receptacle for two appliances located within the dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug-connected in accordance with 400.10(A)(6), (A)(7), or (A)(8)
(4) Nongrounding receptacles used for replacements as permitted in 406.4(D)(2)(a)
2017 code requires all 15 & 20A 125/250V receptacles in the following areas to be tamper-resistant.
As I interpret the code, a garage, detached or otherwise, or similar outbuilding / structure would be covered under 210.52(G), which falls within the areas requiring tamper-resistant receptacles under 406.12(1).
Just my two cents. It would be best to consult your local inspector, as their interpretation of the code may be different, but more than likely, most areas which have adopted 2017 code will require TR receptacles in garages or similar outbuildings.

We have really gotten "dumbed down. I grew up in a house with knob and tube wiring. 30 amp service and two prong outlets. Still alive and the house is still standing. Back then, us kids were taught to leave the outlets alone. We didn't mess with anything that we weren't supposed to. Mom and Dad made sure of that. We were "raised" back then. Now our world is filled with "idiot stickers" and "lawsuits" What the heck happened? Yes, I raised my daughter the same way. She is a happy, mature mother of her own two daughters. She found a husband with the same attitude. Seems to be a dying way of living.
Oh give me a break. Outlets being dangerous isn't a problem for kids 5+ years old. It's for infants and toddlers. It's pretty difficult to tell a toddler who barely understands English and has an attention span of 3 seconds to not stick something in an outlet.We have really gotten "dumbed down. I grew up in a house with knob and tube wiring. 30 amp service and two prong outlets. Still alive and the house is still standing. Back then, us kids were taught to leave the outlets alone. We didn't mess with anything that we weren't supposed to. Mom and Dad made sure of that. We were "raised" back then. Now our world is filled with "idiot stickers" and "lawsuits" What the heck happened? Yes, I raised my daughter the same way. She is a happy, mature mother of her own two daughters. She found a husband with the same attitude. Seems to be a dying way of living.
We have really gotten "dumbed down.

If I am NOT doing any electrical work, must I swap out my existing receptacles for TR units?
If I am adding a receptacle to an existing circuit, which receptacles must be TR; the added one, or all of them?
I think I know this one, but if I am adding a new circuit, must all the receptacle be TR?
For what it is worth, the house is 1880's era, with most of the electrical redone by my Dad in the 1960-70's. Most of the wire he installed in the plastic Romex, but some of the wire that he didn't touch is the spiral metal clad stuff.
.
Now that might get quote of the year even though we have along way to go.Seems to be a dying way of living.
so commercial or industrial dont need non-TR receptacles?Just my $0.02 rant. F the code language. It could easily simply say any new 123abc receptacle in any residence or garage requires a TR.
PERIOD
Exceptions are . . ..
But no.
Every single source regarding this refers to another part of the code. Fail.
There, I feel much better.
Why are non TR outlets even on the shelves at box stores in areas where almost all use is for brand new tract homes ?
I didn't start that way. It was with the left hand, not the rightI also had a few with Alfred E. Nuemann's picture on them
Because some people, like me, and others like me, refuse to use those P.O.S. TR's in their own homes. Just like AFCI's. If I'm installing a new circuit in my house, you can bet on the fact that there will be a $5 breaker at the beginning of the circuit and there won't be a TR receptacle at the other end of it.Why are non TR outlets even on the shelves at box stores in areas where almost all use is for brand new tract homes ?
NEC 406.4(D)Why are non TR outlets even on the shelves at box stores in areas where almost all use is for brand new tract homes ?
I did that as a small child. Only it was a bobby pin instead of a knife. One side in each slot. I remember my thumb was black from some soot but luckily that was about it. Don't remember much else as I was pretty young - don't know how young.