Good morning everyone. I am planning on installing buried cable for my detached workshop. I plan on 100A (110 / 220) service run 175'. I will be doing all the work myself...I'm not an electrician but retired from the USAF in electronics and worked as an electrician apprentice for a couple years. Finding reliable contract work in my area is a big problem for some reason.
I'd like to simply use buried feeder cable but want suggestions. 2' depth, 2 2 2 4 AL MHF or URD with conduit above ground and #6 wire and 2 ground rods / 6' apart and not tied to the subpanel common at the workshop. ???
I'd like to start my run by tapping onto the main service disconnect located beside the meter box. It is a 200A disconnect with feed thru to the main panel inside of house. I've read replacing that panel with a QO1816M200FTRB type (as an example). I'd appreciate any advice on how best to accomplish this and of the overall project.
Much thanks!Service Disconnect.jpg
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,238
Location
Modesto, CA
so you want to tap in on the load side of the breaker?

that can is way to small to make splices in...

also depending on what you will be running, #2 AL is a little small for 175' run...
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
Wylie, can he use a double lug like this that will take #1? This one says it will fit 1/0.

XizRuchqSh757R3Isa6um7QwiLSBiBS011hxADg5Y&usqp=CAc.png
More importantly, do they make one that is offset? How about stacked?
However, if it's box fill that's the problem just ignore the question.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,238
Location
Modesto, CA
Wylie, can he use a double lug like this that will take #1? This one says it will fit 1/0.

XizRuchqSh757R3Isa6um7QwiLSBiBS011hxADg5Y&usqp=CAc.png
More importantly, do they make one that is offset? How about stacked?
However, if it's box fill that's the problem just ignore the question.
i wouldnt want to use that since you have no way to properly insulate it from the metal enclosure
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,876
Location
NW Iowa
Space is going to be the biggest energy. I've done it once where I stripped the insulation back a couple inches on the existing wire, slid a Polaris connector over it, and added my tap to the second hole.

Didn't take up too much extra room
 
OP
T

TxCobra98

Member
Joined
Nov 15, 2020
Messages
6
Location
South Carolina
Space is going to be the biggest energy. I've done it once where I stripped the insulation back a couple inches on the existing wire, slid a Polaris connector over it, and added my tap to the second hole.

Didn't take up too much extra room
So I should be able to come through the bottom of the panel with 1/0 Al using Polaris Connector on the load side?
 
Last edited:
OP
T

TxCobra98

Member
Joined
Nov 15, 2020
Messages
6
Location
South Carolina
Thanks for the replies. So, I'll use the 1/0 1/0 1/0 Al Triplex URD cable tapped (using the Polaris 3 Tap connectors) from the load side of the service disconnect (given enough room if not I'll research for a different panel); buried 24". Conduit on the above ground both inside / outside to each panel...with insulating bushings (as advised). Sound like a good plan? Again very much appreciated.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,238
Location
Modesto, CA
Thanks for the replies. So, I'll use the 1/0 1/0 1/0 Al Triplex URD cable tapped (using the Polaris 3 Tap connectors) from the load side of the service disconnect (given enough room if not I'll research for a different panel); buried 24". Conduit on the above ground both inside / outside to each panel...with insulating bushings (as advised). Sound like a good plan? Again very much appreciated.
You need a 4-wire feeder and single rated URD is not rated for or permitted to be inside structures.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,123
Location
Central Iowa
Are you worried that the PVC conduit is going to rub through the insulation?
NEC 300.4(G) states that wire #4 and larger need to be protected when entering an enclosure. It lists four ways to do it, but a bushing is the easiest and most common. Contrary to what many people think, including journeyman with many years experience, there is no exception for PVC.
 
To avoid these ads, REGISTER NOW!

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,901
Location
Southern Oregon
Thanks for the replies. So, I'll use the 1/0 1/0 1/0 Al Triplex URD cable tapped (using the Polaris 3 Tap connectors) from the load side of the service disconnect (given enough room if not I'll research for a different panel); buried 24". Conduit on the above ground both inside / outside to each panel...with insulating bushings (as advised). Sound like a good plan? Again very much appreciated.
You're feeding from the load side of a 200A breaker. The wire needs to be sized for the breaker. The breaker in the shop panel only serves as a disconnect.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,993
Thanks for the replies. So, I'll use the 1/0 1/0 1/0 Al Triplex URD cable tapped (using the Polaris 3 Tap connectors) from the load side of the service disconnect (given enough room if not I'll research for a different panel); buried 24". Conduit on the above ground both inside / outside to each panel...with insulating bushings (as advised). Sound like a good plan? Again very much appreciated.

just put a feed-through panel in. you'd gona have a hell of a time with that space.


1668171270997.png


then run 100a of service to the shop via a breaker.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
You're feeding from the load side of a 200A breaker. The wire needs to be sized for the breaker. The breaker in the shop panel only serves as a disconnect.
If it's all outdoors (such as this is) you're allowed feeder taps of an unlimited distance.
NEC 240.21 (5)
 
Last edited:
OP
T

TxCobra98

Member
Joined
Nov 15, 2020
Messages
6
Location
South Carolina
Where does he say that? It starts outdoors, and if he place a disconnect outside of the proposed shop that portion will satisfy the rule. If he uses URD instead of MHF it's not even allowed inside

He's right...I was planning on running it inside but I'll do as you suggest and place a disconnect outside the workshop. I may also do as jeepxj suggests and add a feed-through panel in place of the service disconnect at the house. I also will use:

1/0-1/0-1/0-2 Notre Dame Quadruplex Aluminum Conductor Underground Direct Burial 600V URD

Thanks everyone and thanks to all you veterans for your service.

 

Walkers

Well-known member
Joined
May 17, 2021
Messages
3,912
Location
Cave Creek Az
NEC 300.4(G) states that wire #4 and larger need to be protected when entering an enclosure. It lists four ways to do it, but a bushing is the easiest and most common. Contrary to what many people think, including journeyman with many years experience, there is no exception for PVC.
Interesting. Have you ever seen it cause a problem, or is it just a gotcha in the code because it wasn’t specifically written?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,123
Location
Central Iowa
Interesting. Have you ever seen it cause a problem, or is it just a gotcha in the code because it wasn’t specifically written?


I don't recall ever actually seeing it happen, but I can see it happening. The ends of the PVC adapters aren't razor sharp but they are sharp enough that if the wire was bent tight enough over the edge and given enough time, it could cut through the insulation.

It's not really a gotcha because it covers all wiring methods where #4 and larger wire is used. People just assume PVC doesn't need a bushing because it's PVC.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,560
Location
SE MI
Good morning everyone. I am planning on installing buried cable for my detached workshop. I plan on 100A (110 / 220) service run 175'.
Ask yourself AGAIN, "Do I really need 100A ?". Most 1 man shops can I easily get by on 60A. You would save a lot of $$$ on a $175' run.

DO IT RIGHT ! Replace that load center with a 2-6 position 200A one and install a ground.
 

Fasthotrod

Well-known member
Joined
Dec 14, 2015
Messages
218
Location
Oklahoma
Interesting. Have you ever seen it cause a problem, or is it just a gotcha in the code because it wasn’t specifically written?
I have not seen it cause a problem with PVC damaging the conductors, but the Code doesn't specify that PVC conduit is excluded. A sharp inspector will see it and call you on it. (That, I have seen before.)
 
OP
T

TxCobra98

Member
Joined
Nov 15, 2020
Messages
6
Location
South Carolina
Ask yourself AGAIN, "Do I really need 100A ?". Most 1 man shops can I easily get by on 60A. You would save a lot of $$$ on a $175' run.

DO IT RIGHT ! Replace that load center with a 2-6 position 200A one and install a ground.
1668522830624.png
SIEMENS W0404MB1200CT 200 Amp Outdoor Trailer Panel, Gray


I'd like to use this in place of the current disconnect.
 
To avoid these ads, REGISTER NOW!