Does anyone know what KCP&L supplies in the KC area for a temporary power tap while upgrading a service?
I am upgrading my electrical service from a 100A FPE panel to a 200A Siemens panel. The power company, KCP&L, is providing a "temporary power tap" while I am doing the work. I can find their definitions of a "construction tap" which consists of a pole, meter, and a couple 120VAC outlets. What I think I need is a meter with a couple outlets AND a 30-40A breaker with a SO cord of some type that I can use to power my circuits temporarily in several configurations while I work. It is freezing cold outside!!! I could turn the 30-40A breaker on and off as required while I work. A lockout box would be nice.
I have about 40' of triplex from the pole to the mast. I am planning on using a 2" rigid conduit mast and weatherhead. #2/0 copper power conductors with a #4 copper grounded conductor. I need 18" of clearance over my roof overhang so I figure 30" of conduit above the roof will do the job with drip loop etc. I have #6 solid copper wire running to my water pipe. I also have a #6 solid copper wire to my 10-12' long 1/2" diameter copper clad supplemental electrode driven below the meter box itself. The supplemental electrode is connected to ground in the meter box at the moment. KCP&L now says they do not allow that. Could I clamp it to the #4 copper grounded conductor in the LB below the meter before the conduit enters the house? I would like to have as close to a straight shot to ground as I can get for lightning transients.
I will probably use PVC ENT for the run from the meter box to the panel just for ease of fabrication. It is close to being a straight drop from the meter to the main panel in the basement. Three LB's will probably do the job.
There is another ground rod placed by the telephone company about 20' away from the meter and maybe 35' from the water line. Do I need to bond to that ground rod also?
The transformer at the pole is only 15KVA and serves two dwellings with 100A service. If my calculations are close that is only about 60A, or 30A per residence. I have a welder, kiln, lathe, mill, and a real 3HP compressor. I can see needing 130A for several minutes at a time. I have been getting by by running around and making sure stuff is off. The ex messed me up while welding by turning on the oven once. Will KCP&L upgrade the transformer at the same time? I don't want to fry the transformer and put me and my neighbor out of power when it is 105°F outside.
Am I doing it correctly?
Thanks for your help. I can design and build machine controls and large motor control centers for use in the US, Europe, or elsewhere, but residential NEC conditions are confusing.
The KCP&L electric service manual:
http://www.kcpl.com/newconst/ess.html
I am upgrading my electrical service from a 100A FPE panel to a 200A Siemens panel. The power company, KCP&L, is providing a "temporary power tap" while I am doing the work. I can find their definitions of a "construction tap" which consists of a pole, meter, and a couple 120VAC outlets. What I think I need is a meter with a couple outlets AND a 30-40A breaker with a SO cord of some type that I can use to power my circuits temporarily in several configurations while I work. It is freezing cold outside!!! I could turn the 30-40A breaker on and off as required while I work. A lockout box would be nice.
I have about 40' of triplex from the pole to the mast. I am planning on using a 2" rigid conduit mast and weatherhead. #2/0 copper power conductors with a #4 copper grounded conductor. I need 18" of clearance over my roof overhang so I figure 30" of conduit above the roof will do the job with drip loop etc. I have #6 solid copper wire running to my water pipe. I also have a #6 solid copper wire to my 10-12' long 1/2" diameter copper clad supplemental electrode driven below the meter box itself. The supplemental electrode is connected to ground in the meter box at the moment. KCP&L now says they do not allow that. Could I clamp it to the #4 copper grounded conductor in the LB below the meter before the conduit enters the house? I would like to have as close to a straight shot to ground as I can get for lightning transients.
I will probably use PVC ENT for the run from the meter box to the panel just for ease of fabrication. It is close to being a straight drop from the meter to the main panel in the basement. Three LB's will probably do the job.
There is another ground rod placed by the telephone company about 20' away from the meter and maybe 35' from the water line. Do I need to bond to that ground rod also?
The transformer at the pole is only 15KVA and serves two dwellings with 100A service. If my calculations are close that is only about 60A, or 30A per residence. I have a welder, kiln, lathe, mill, and a real 3HP compressor. I can see needing 130A for several minutes at a time. I have been getting by by running around and making sure stuff is off. The ex messed me up while welding by turning on the oven once. Will KCP&L upgrade the transformer at the same time? I don't want to fry the transformer and put me and my neighbor out of power when it is 105°F outside.
Am I doing it correctly?
Thanks for your help. I can design and build machine controls and large motor control centers for use in the US, Europe, or elsewhere, but residential NEC conditions are confusing.
The KCP&L electric service manual:
http://www.kcpl.com/newconst/ess.html