I am running a brand new 20 amp 12ga circuit that I have wired up in my garage with 16 outlets (a lot of points for potential wiring mistakes) and I am looking for a way to test it before I go live. The first outlet in line from the breaker box is a cgfi the rest are regular.

Am I correct in thinking that a continuity test between the two blades in a single outlet should be open? Does the cgfi effect this?
 
To avoid these ads, REGISTER NOW!

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
I always check the wires as I go along --then turn it on. I check each outlet with one of the plug in testers to make sure I have a ground and nothing is wired backward. If you check as you go along you should have no problems. The breaker will immediately click if you have an issue with the hot.

I don't use the outlet for the connections -- I do the connections and use pigtails to the outlet.

In my area 10 outlets is the max on a feed.
 

3rdgen

Well-known member
Joined
Jan 26, 2013
Messages
144
Location
London Ont
If you take you black and white wires from the panel feed and ring them out with a continuity meter and get nothing then go from the hot to ground you should be good as far as breaker triping, It may also be a good idea to buy yourself a receptacle tester as well just to double check your wiring when the powers is on.
 

kd3pc

Well-known member
Joined
Aug 10, 2013
Messages
3,630
Location
Northern Neck
I wire the device and then leave it un attached to the box, then power up and walk them and test them as I go....turn off power and install them and plates.

good to go.
 

Beemer533

Well-known member
Joined
May 9, 2014
Messages
2,057
Location
Syracuse, NY
If you really want to test it without power, a simple continuity check would work fine.

I'm pretty sure 16 devices on one breaker is too many. I would have run 2 circuits for that many outlets.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,652
Location
SE MI
Flip the breaker ! If anything is seriously wrong. the breaker will trip.

Use an outlet tester to verify all receptacles.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
If residential & under the NEC, it's code compliant, if non-residential it's not, but code compliant does not always equal a good install, it's a minimum standard.
 

Beemer533

Well-known member
Joined
May 9, 2014
Messages
2,057
Location
Syracuse, NY
If residential & under the NEC, it's code compliant, if non-residential it's not, but code compliant does not always equal a good install, it's a minimum standard.

I would definitely not have guessed that.. I thought the max was closer to 11.

Either way, I wouldn't do it.
 
OP
H

Honest Bob

Well-known member
Joined
Jul 3, 2010
Messages
263
Location
Easton, PA
Thanks guys! I ended up just flipping the breaker, everything was wired right. It does seem to be to many outlets to be on one circuit, but to be honest putting quads everywhere was probably overkill. I cant see having more than a light bulb and one power tool being used on that circuit at once.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
For commercial the magic number is 180 VA per strap or yoke, up to three receptacles per, if there are four or more receptacles, its 90 VA per receptacle. For a 20 amp/120v circuit, that works out to 13 receptacles.

Charles
 

James-W

Well-known member
Joined
Feb 3, 2013
Messages
12,432
Location
Southeastern Wisconsin
When I built my garage I decided to only have 4 outlets per circuit breaker and the first outlet in each circuit is a GFCI which around here is a requirement for a garage.
 