Testing a 240 Line

Theruse

Well-known member
Joined
Aug 12, 2012
Messages
341
Location
Maryland
Need to check if my electric clothes dryer is getting power. I have a two wire circuit tester that I use for 120v to check for power. Can I use this for a 240v line and more importantly, which two contacts. It is a threw prong outlet.
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,500
Location
Richmond, VA
Very likely the tester is rated for 300 or 600v. Post a pic or model number. It should also say on it.

A pic of the plug would help too. Worst case if you go hit to ground, you'll get 120v, but it won't hurt anything.
 
OP
T

Theruse

Well-known member
Joined
Aug 12, 2012
Messages
341
Location
Maryland
240voutlet.jpg

Mike,

When you say it won't hurt anything, I hope that includes me! I will test one flat angled blade to the center ground to check for 120v and do the same for the other angled blade to the ground. At work now, so will check this evening. Thanks again.
 
OP
T

Theruse

Well-known member
Joined
Aug 12, 2012
Messages
341
Location
Maryland
That's what i intend to do is test each leg against the ground. I don't have my simple tester with me, so not sure what it is rated for 120 or both 120 and 240
 

jayoldschool

Well-known member
Joined
Apr 23, 2006
Messages
2,119
Location
Canada
You don't have a DVOM? You need to get one... Set it to 300V, probes in both sides. A cheap HF one will work fine.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
240voutlet.jpg

Mike,

When you say it won't hurt anything, I hope that includes me! I will test one flat angled blade to the center ground to check for 120v and do the same for the other angled blade to the ground. At work now, so will check this evening. Thanks again.

To confuse things more the outlet pictured is an ungrounded dryer outlet. Technically the "L" shaped hole is neutral. Should get 240V across the two flats and 120V between one or the other flats and the "L".
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
Be careful doing this. If your dryer is not working it may be that the outlet is wired incorrectly. I'd turn off the power and pull it out to see what's going on, or off, as it were.

59020.jpg


Almost all of these inexpensive testers will test 90 to 300v. Some to 250v only. Do examine and read any data on the device. Therefore, you can test across the hots.
 
OP
T

Theruse

Well-known member
Joined
Aug 12, 2012
Messages
341
Location
Maryland
The 240v dryer outlet has worked fine for years. What prompted all this trouble was no power to a 120v outlet in garage. It turned out that the garage outlet was connected to a line that had a GFCI in an outlet in a spare bathroom (rarely used) at the opposite end of the house. At one point, I turned off all fuses and reset them before I found the culprit GFCI. That is when the dryer stopped working.
 
To avoid these ads, REGISTER NOW!

PelicanPines

ALLIANCE MEMBER
Joined
Apr 30, 2014
Messages
38,112
Location
New Jersey, USA, Earth, My own reality
Bad breaker?

Dryer should be dedicated.

What brand of panel do you have?

If everything was always done perfectly... diagnostics would get used less...

I have personally found issues with dryers that were wired from two independent breakers... I also found a 120v outlet wired with TWO FREAKING HOTS on TWO breakers... with one of the hots CUT at the edge of the box... so I didn't know it... till I started to cut the BX... and got zapped... way back then... they didn't have surface/above wire voltage testers.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
If this happened after switching off the breakers, I'd replace the breaker. They are not big $. Case in point, had a GFCI go out on the bench plug circuit 2 weeks ago. Switched off run, replaced GFCI, breaker on. What, no power. Switch off, take outlet apart again, make sure I didn't futz the wiring, breaker on - test. Power. OK, WTF. Breaker off, re-assemble box, power on - no power. WTF. Pull panel cover, test at breaker - works sometimes, sometimes not. Breaker is 6 years old. They's just things and things break.
 
OP
T

Theruse

Well-known member
Joined
Aug 12, 2012
Messages
341
Location
Maryland
That's my thinking is that it is a bad breaker. Only thing I did differently to cause this is turn all the circuits breakers off than on. Just to make sure it was not the dryer, I tried to reach my dryer plug to my 240v outlet in the garage used for my Bendpak lift. Unfortunately, I need three feet more.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
240voutlet.jpg

Mike,

When you say it won't hurt anything, I hope that includes me! I will test one flat angled blade to the center ground to check for 120v and do the same for the other angled blade to the ground. At work now, so will check this evening. Thanks again.

There is no ground in the receptacle shown above, it is a non-grounding 125/250 volt rated device, so the "L" shaped slot is a neutral.
 
OP
T

Theruse

Well-known member
Joined
Aug 12, 2012
Messages
341
Location
Maryland
Checked it out and only one side is hot. Either I have part of the breaker not working or a wire loose. So tomorrow heading to HD for a new breaker as I suspect since this happened after I switched the breaker on and off. Thanks everyone for the tips today.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
10,954
Location
Rhode Island
I recently had a new-ish (~7 year old) Square-D homeline 30A double-pole breaker fail in the same manner. Breaker tripped and when I reset it, only one side came back up.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,500
Location
Richmond, VA
Checked it out and only one side is hot. Either I have part of the breaker not working or a wire loose. So tomorrow heading to HD for a new breaker as I suspect since this happened after I switched the breaker on and off. Thanks everyone for the tips today.

make sure you get a breaker that is listed for your panel and not just one that fits. take a picture of the label in your panel and only bring the existing breaker with you if it matches the label.
 

6PTsocket

Well-known member
Joined
Mar 12, 2014
Messages
4,593
To confuse things more the outlet pictured is an ungrounded dryer outlet. Technically the "L" shaped hole is neutral. Should get 240V across the two flats and 120V between one or the other flats and the "L".
Right you are. I had to look it up. It is a NEMA 10-30. I guess the 240 is for the heat . They probably use 120 for the electronics. And I have no idea about the motor. That must mean they need a ground wire for the machine. I find it hard to believe they don't use a 4 wire plug to bring in a ground.

Sent from my SM-G900V using Tapatalk
 
OP
T

Theruse

Well-known member
Joined
Aug 12, 2012
Messages
341
Location
Maryland
All fixed. It turned out to be a bad Square D Q0 breaker. Not sure why Q0 is twice the price of homeline. But $16 is a lot cheaper than calling the electrician so not complaining.
 