Keyblazer
Well-known member
My Garage upgrade is moving forward and I am planning my lighting/power upgrades.
This Garage has 2 power outlets,#1 is the original one(I think) by the door into the house and #2 by the garage door, which I think was added.
I wanted to know what breaker these were on, and how much power I had, so I bought a circuit locator.
I plugged the locator into #2 and found the breaker it is fed by(15A) no prob, but when I do the same with #1, it does not show up which breaker feeds that circuit.
What is also odd, is that #2 starts my 110V compressor fine, and allows me to use my Welder no prob, but if I put the compressor into #1 recepticle, it will not start... spins slow, then kinda browns out and pops the breaker, so I know which one feeds it.
Ideas as to what the prob is with #1?
Oh, FYI I put one of those "diagnostic" plugs into #1 to check for bad wiring and it shows up as good.