While the pressure test methods will work to find most leaks, and certainly all "dangerous" leaks, unless required by code I wouldn't do that. I'd use leek-seek or another leak detection fluid on all the threads and fittings once they are under gas pressure. You'll find any "fizzer" leaks with soap that will never show up in a pressure test.
That's what I'd do. I'm not telling you what you should do.
One thing I will tell you to do is check any appliance connectors documentation to make sure they'll take your test pressure before you put 100 psi on one. Standard service pressure for natural gas is 0.25 psi. Putting 400 times that pressure on it might be a problem.
My experience is if it leaks at 25 psi...it will still leak at 0.25 psi....just not as much. In any case, you can find leaks with soap that are undetectible by any other means short of a flame ionization detector.
Phil