I've read 50 different posts on here with 10 different answers on the proper wire to use for a subpanel.

My run is about 50'. I'm using copper. If I go 60 amp, I have to use 4 gauge. Since I never see needing more than 50 amps, I'm going to go 50 amp so I can use 6 gauge copper.

I know separate busses for neutral and ground, ground rod at subpanel, run 4 wires between panels, etc. I know max height for the subpanel. I know that if I run conduit, I have to bury to 18", and if I run direct burial, I have to bury at 24" with conduit risers on both ends. I'm governed by the 2005 NEC where I live.

There is a considerable amount of conflict over what type of wire to run. Some say run SER wire inside conduit. Others say SER isn't specifically permitted by NEC, so it's prohibited. I know that even in conduit, it has to be wire permitted for wet locations. So what's the optimal wire solution here? 6-3 what?

Should I just run 6-3 UF in the conduit (outside) and be done with it? The advantage here seems to be that I would not have to run conduit inside the house; could just route the wire through the joist space.

Or should I pull individual conductors in conduit? (and if so, that would be THNN, correct?) That would mean running conduit for the full length of the run.
 
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,078
Location
Minneapolis
That's the fun part about electrical work - there isn't necessarily only one right answer. :)

UF will work, but it will be a little difficult to pull through conduit, plus you have to make sure the conduit is sized correctly.

THHN/THWN will be easier to install in conduit. You can include a junction box where the conduit comes into the house and transition to NM at that point for indoors.

edited to change from UF to NM...I hadn't had my coffee yet.
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The easiest is to run the #6 UF from panel to panel. Do direct bury with conduit raisers. The #6 UF is okay for 55A so technically you can breaker it at 60A. Or do as Stuart suggested using THHN/THWN in conduit outside and NM-b inside.
 
Last edited:
OP
L

lawfarm

Well-known member
Joined
Jul 12, 2008
Messages
719
Location
NorCal
Other than the inconvenience of pulling UF in conduit, there's no reason I couldn't just run the full distance in UF (conduit outside, joist space inside) and avoid the inside junction box, right?
 
To avoid these ads, REGISTER NOW!

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
13,753
Location
Lebanon, TN
Full distance in UF is fine. It's a ****** to pull and a ****** to strip back to individual conductors at the termination points.
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Other than the inconvenience of pulling UF in conduit, there's no reason I couldn't just run the full distance in UF (conduit outside, joist space inside) and avoid the inside junction box, right?

If you read my post, I said you can run the UF from panel to panel. That means no splices needed.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
I've read 50 different posts on here with 10 different answers on the proper wire to use for a subpanel.


Thats because every install is slightly different and there is multiple ways to do it.

My run is about 50'. I'm using copper. If I go 60 amp, I have to use 4 gauge. Since I never see needing more than 50 amps, I'm going to go 50 amp so I can use 6 gauge copper.

Where did you come up with needing #4 for 60a? Maybe youre thinking of aluminum? :dunno

You can use #6 THWN, rated for 65a, for 60a branch feeder...

I know separate busses for neutral and ground, ground rod at subpanel, run 4 wires between panels, etc. I know max height for the subpanel. I know that if I run conduit, I have to bury to 18", and if I run direct burial, I have to bury at 24" with conduit risers on both ends. I'm governed by the 2005 NEC where I live.


You will need 2 ground rods.

And if youre under the 2005 NEC, then you only need 3-wire but i would still do 4-wire for safety reasons.

There is a considerable amount of conflict over what type of wire to run. Some say run SER wire inside conduit. Others say SER isn't specifically permitted by NEC, so it's prohibited. I know that even in conduit, it has to be wire permitted for wet locations. So what's the optimal wire solution here? 6-3 what?

Ive never understood the debate conflict and confusion about SER being prohibited for use underground. But alas, it CANNOT be ran underground.

Should I just run 6-3 UF in the conduit (outside) and be done with it? The advantage here seems to be that I would not have to run conduit inside the house; could just route the wire through the joist space.

Or should I pull individual conductors in conduit? (and if so, that would be THNN, correct?) That would mean running conduit for the full length of the run.

If it were mine, I would use #2 AL MHF in 2" conduit and transition to al SER inside the house.

Using #6 cu with a #10 ground will cost you almost 3 times what MHF costs per foot. $3 vs $1.17

and UF-b is almost $4/ft so....
 