Im new here and this is my first post. I recently hired a handyman to help me with some wiring issues and now, I fear he's done it all wrong. I will try to post some pictures.
 
To avoid these ads, REGISTER NOW!
OP
J

jbird007

Member
Joined
Jan 9, 2014
Messages
6
Pic 01 shows the meter on the pole with power running to the box with the pull out fuses underneath. From there, power runs down the pole underground, up the trailer and into the fuse box in the bedroom closet. Power also runs from pull out fuse box to the fuse box with the round fuses right next to it.
Pic 02 shows the grounding rod
Pics 03 and 04 show close-ups of the meter and box.
Pics 05 and 06 show closeups of one the pull out fuses.
Pic 07 shows the fuse box that im getting rid of. The lever is broke, but it still works.
Pic 08 shows the fuse box in bedroom closet.
Pic 09 shows the water heater.
Pic 10 shows the power going up the pole from fuse box in pic 07.
Pic 11 shows power coming from high on the pole to the top of the hut, then to the front of the trailer.
Pic 12 shows the power going in the front of the trailer, where it feeds the hot water heater and light above sink.
 
OP
J

jbird007

Member
Joined
Jan 9, 2014
Messages
6
Pics 13 and 14 show my new breaker box.
Pics 15 and 16 show my new wire.
Pic 17 shows my new GFCI outlet, that i want to run first with this switch in the same box under he breaker box.
Pic 18 shows the switch wire running behind the breaker box and up to the light fixture.
Pic 19 shows where the light fixture will go and continues on down to where the ceiling fan/light will go.
Pic 20 shows where the ceiling fan/light will go.
Pic 21 shows where i put a couple staples in.
Pic 22 shows the holes i cut out of my ceiling, lol.
Pic 23 shows the power going down to the last outlet on the circuit.
Pic 24 shows 2 gang box under panel wired with GFCI outlet and light switch
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
I'm not sure what you are asking. I see very little new work that can be commented on.

Two biggies I see are WHY a main lug panel? And that 3-wire URD you got is not right. You need a 4-wire feeder cable, with a separate ground wire, and also you need a ground rod at the separate structure. Or is that a trailer?? I see what looks like a trailer outside, then I see what looks like a block wall and framing inside.
The pics are not very good to let us know what's going on.
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I got to agree with Speedy on this. Even all kinds of maintenance electricians are not familiar enough with codes and just havnt done the new service install work with inspections to get it right.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I got a call a while back from a plumber and at first I thought dumb azz but on further reflection I could see the confusion, it wasn't as straight up as adding a breaker wire to the water heater but was to an lod fuse box (with ample capacity) but needed to be tapped with local ocpd in this case etc that is although simple can get fu upped. Didn't understand some of these installs when I was a kid, most are gone but,,, on occasion have an inspection turn down to fix and its not always an owner but often handyman work.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Did one last spring, the handy did a fair job but missed some wire protection, some bushings and landed the N and G on the same bar in the sub,, with no bond to the can, the branches were grounded (not separately)but,,, I went home and got a bar, some pipe for the riser, got 1 N under a screw, put in 2 gfci and a switch to an entrance in a shed as I recall. I must have opened the box at the main to make sure it wasn't double wired under screws.

He had all the grounds twisted, I see a wire landed on the devices, didn't check it all. I had a helper and it still took better than a couple hrs to fix most of the violations. Added a rod too.

I ran across a couple un grounded boxes lately.
 
Last edited:
To avoid these ads, REGISTER NOW!
Top Bottom