There must be an easy solution bcuz electrician are brilliant

Jcrapola

Well-known member
Joined
Mar 12, 2013
Messages
147
Location
North of Detroit
So I just had my 30x 40 post frame building put up, and now I am trying to run wire for my sub panel. I ran about 70’ of 1 1/2” PVC conduit underground (24” deep) to the new structure. I am at a loss for how to get the wire from the main panel in my basement into the conduit. I am planning to use an LB elbow at the end of the conduit (outside) and push a piece of conduit thru the wall (brick, sheathing, and a 2x12 that is on top of my poured basement wall). The issue is my main panel already uses all the knockout holes on the top of the panel for the house wiring and the feed from outside. So, I need to run the wire down and into a knockout in the side of the panel. But, I cannot conceive of how to make the turns required from the thru hole from outside to the knockout.

I was thinking I could terminate the conduit in a 6” enclosure and run 1 1/2” greenfield from the enclosure to the panel knockout. I would not terminate the waives in the enclosure just pull through it into the greenfield. But even typing it makes me feel queasy. It makes me feel like a hack.

I am including a couple pics. The first one is of where I am going to come thru the wall (just under the 2 coax cable lines) and the knockout hole I wish to use on the side of the panel. The second is the top of the main panel to illustrate how little space remains.

I am hoping one of the sparkles will chime in and stop me from being an idiot.
 

Attachments

  • C80647AB-CB7B-47E6-8F06-04004390EC3F.jpeg
    C80647AB-CB7B-47E6-8F06-04004390EC3F.jpeg
    24.7 KB · Views: 130
  • 178D9A56-6CAD-46A3-B290-278D1E97856C.jpeg
    178D9A56-6CAD-46A3-B290-278D1E97856C.jpeg
    24 KB · Views: 127
To avoid these ads, REGISTER NOW!

spudley

Well-known member
Joined
Dec 27, 2016
Messages
702
Location
Northeast Wisconsin
I had a very similar situation and I used a wide sweep 90 from the rim board, then a 45 (and a small piece of conduit) into the box.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
90 sweep from rim joist to LL conduit body into panel. Or LR or LL body from rim joist to a LL body into panel. Hopefully I got my body order correct.
 
Last edited:
To avoid these ads, REGISTER NOW!

Two Sheds

Well-known member
Joined
Jan 16, 2014
Messages
101
Just be aware that if you decide to use a pull box, it needs to be sized per 314.28, and will likely be bigger than you expect. You'll be better off if you can use a conduit body.
 

Raisedonadeere

Well-known member
Joined
Jul 31, 2017
Messages
436
Location
Central KY
FWIW I have been amazed at how much easier a pull through a 45 is than a 90. I redug a ditch to allow use of a 45 in a place there had been a 90. wow what a difference. Even two 45s separated a bit is easier than a 90. I don’t know that to be true in all size combinations. Just saying if something doesn’t work try something else.
 