Does a thermostat jump the Y and G together when in the cool position? I assume it does not do this in the heat position. I ask as working on a Rheem rooftop unit on my building today I had to look over the wiring diagram and cannot find how the room blower relay in energized in the cool position. Older RRGG unit.
 

Attachments

  • RRGG Wiring.pdf
    76.9 KB · Views: 14
To avoid these ads, REGISTER NOW!

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
Most thermostats jump both Y and G to R for cooling. Some thermostats have a setting or switch for gas or electric heat. When set to electric heat they jump W and G to R for a heat call. When set to gas only W is connected to R.

I think that electric heat switch doesn't apply to you as the diagram shows FCC which looks like a fan and limit switch. It turns on the blower when the temp gets high enough. Also cuts power to the gas valve if over temp.
 
To avoid these ads, REGISTER NOW!

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
That unit uses a single speed indoor blower motor, not a multi speed blower motor like a residential unit. There is no need to tie "Y" & "G" at the thermostat. The thermostat energizes the blower relay on a call for cooling, closing the blower relay Normally Open contacts (B2). On a call for heat, the blower relay is not energized. There is a thermostatic switch (FCC) that energizes the indoor blower motor through the blower relay Normally Closed contacts (B5) when the heat exchanger reaches a preset temperature.

Tommy
 
Last edited:
OP
P

Paperman

Well-known member
Joined
Feb 19, 2014
Messages
148
Location
On the shore of LK Michigan
That unit uses a single speed indoor blower motor, not a multi speed blower motor like a residential unit. There is no need to tie "Y" & "G" at the thermostat. The thermostat energizes the blower relay on a call for cooling, closing the blower relay Normally Open contacts (B2). On a call for heat, the blower relay is not energized. There is a thermostatic switch (FCC) that energizes the indoor blower motor through the blower relay Normally Closed contacts (B5) when the heat exchanger reaches a preset temperature.

Tommy

So that leads me to believe yes the thermostat has internally tied the y&g together as it seems that is how you describe it functioning. The wiring diagram was not make sense but now knowing that i have it straight in my head. Thank you all.
 