Hi,

A nest thermstat e was installed last summer by an AC technician.
Today I found there is no aux heat in the thermostat and it only allows heat pump heating. By the way, my house has a heat pump and a gas heater.

I did google search about it and it looks like there is a wiring issue.

What I found on google is that aux heat is white wire. However, when I opened the thermostat, I found the white wire was not connected. I went downstairs and found the white wire from the air handler is not connected to the white wire to the thermostat. Instead, it is connected to the green wire from the compressor that I believe it is a safe ground.
I don't know why they are wired in that way.
Could you please see the attached picture and let me know whether I can just detach the green from the white and connect the white to the white from the thermostat?
Thanks!
DS
 

Attachments

  • thermostat wiring.jpg
    thermostat wiring.jpg
    121.3 KB · Views: 62
To avoid these ads, REGISTER NOW!

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
He sold you the wrong t-stat. You have a t-stat for a heat pump without aux heat. You need a W2 terminal to have aux heat. Not sure what he did with the wiring just by looking at the pic. I'd need to see the terminal board connections in the units.

Tommy
 
Last edited:
To avoid these ads, REGISTER NOW!

BD1

Well-known member
Joined
Mar 18, 2007
Messages
4,602
Location
north side
Call tech support for thermostat if instructions are confusing.


Sent from my iPhone using Tapatalk
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,996
Location
Peace Valley,mo
For emergency heat need 6 wires if the stat needs a common.
R power
G fan
W1 white reversing valve
W2 emergency heat
Y cooling
C common

Sent from my KFDOWI using Tapatalk
 