Hello,

I have some three-phase woodworking equipment (two of which are 7.5 HP) that I am powering through a Phase Perfect converter (picture below). The manufacturer recommended just using twist lock plugs/receptacles instead of hardwiring into a disconnect but said I could do either.

I was on the Hubbell website looking at plugs and found that a 3Ø, 30 amp, 250AC plug has a max 3 A/C HP rating with the following footnote: "The horsepower ratings are the phase values." I'm confused by this statement and also don't see other options shown that are any higher than 3 HP.

Any three-phasers or electricians out there that could interpret? Thanks.
 

Attachments

  • IMG_0449.jpg
    IMG_0449.jpg
    72.4 KB · Views: 46
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,586
Location
Fullerton, CA
Receptacle ratings over 3.5HP are available but the are a pin and sleeve product and expensive (almost prohibitively so).
Can you hardwire the machines?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,054
Location
Modesto, CA
Plugs and receptacles for motor circuits must be rated for the same or greater HP as the motor HP rating.

You will not find a standard NEMA twist-lock plug rated for that high amount of HP. As said above, pin and sleeve would be your only option if you must use cord and plug setup.
 
Last edited:

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,586
Location
Fullerton, CA
A pin and sleeve plug generally has a ring around it that mates up with the receptacle that you twist to lock them together. The actual contacts don't move though
shopping
 
Last edited:
OP
B

BentBierz

Well-known member
Joined
Dec 3, 2014
Messages
188
Location
Alvin, TX (Houston Metro Area)
Receptacle ratings over 3.5HP are available but the are a pin and sleeve product and expensive (almost prohibitively so).
Can you hardwire the machines?

Yes, I can hardwire it and that is certainly an option that I am entertaining. I was just surprised to have an engineer from the manufacturer (Felder) tell me that a twist-lock would be fine and then to see there was a HP component to the equation.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,054
Location
Modesto, CA
Yes, I can hardwire it and that is certainly an option that I am entertaining. I was just surprised to have an engineer from the manufacturer (Felder) tell me that a twist-lock would be fine and then to see there was a HP component to the equation.

you know what they say about engineers....

I would never trust an engineer to follow NEC code.

I cant count the times Ive seen architects draw up plans that violated the NEC....
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,737
Location
SE Michigan
Everyone is going to go bananas because of NEC. But:

The twistlock will work functionally fine as long as you don't a) overload the amp rating and b) don't unplug it under load.

Real potential for a nasty arc flash that can damage people, the plug or the receptacle if plugged or unplugged under load. The pin & sleeve connectors I have only seen interlocked to a disconnect so that they can only be mated or un-mated when the disconnect is in the OFF position.
 
To avoid these ads, REGISTER NOW!

W-Cummins

Well-known member
Joined
Jan 9, 2006
Messages
1,641
Location
Iowa
You can use a 15-50p for 7.5hp it's not a locking plug, but way cheaper than a pin and sleeve plug set.
 

W-Cummins

Well-known member
Joined
Jan 9, 2006
Messages
1,641
Location
Iowa
Real potential for a nasty arc flash that can damage people, the plug or the receptacle if plugged or unplugged under load. The pin & sleeve connectors I have only seen interlocked to a disconnect so that they can only be mated or un-mated when the disconnect is in the OFF position.




The design of the pin&sleeve set allows the disconnect under load with the larger pin spacing and also the shroud. I have them with and without the disconnect interlock.


I also have a water proof twist lock setup that is "up rated" to 15hp from 10hp when using the interlock setup, thus making my $$$ extension cord ( not to code:)
William....
 
OP
B

BentBierz

Well-known member
Joined
Dec 3, 2014
Messages
188
Location
Alvin, TX (Houston Metro Area)
You can use a 15-50p for 7.5hp it's not a locking plug, but way cheaper than a pin and sleeve plug set.

Thanks...these might be an option. I have also found some 50 amp locking plugs but unfortunately could not find any HP ratings. Seems like HP ratings are an afterthought when listing specs online. I have seen some listings that say that the item has an HP rating but doesn't say what it is...pretty frustrating.
 

86turbodsl

Well-known member
Joined
Jul 1, 2005
Messages
6,558
Location
Michigan
I was going to respond by telling the OP about pin and sleeve connectors, but since I'm an engineer I guess I better not.

Same here. I don't follow the NEC 100% either. Those guys are ridiculously ****. There's risk in everything. Trying to stop any sort of problem from ever happening costs $$$ to everybody and is a nuisance. don't get me started on arc-fault breakers the assh*les made me put in my house build.
 
OP
B

BentBierz

Well-known member
Joined
Dec 3, 2014
Messages
188
Location
Alvin, TX (Houston Metro Area)
I was going to respond by telling the OP about pin and sleeve connectors, but since I'm an engineer I guess I better not.

in my job in the Coast Guard as a commercial vessel inspection branch chief, i have to deal with engineers (naval, mechanical, electrical, P.E.) all the time and currently have two on my staff. Other than an ocassional knuckle head (smart but no common sense), I would rather have more than fewer working for me.
 

Lightning rod

Well-known member
Joined
Dec 1, 2012
Messages
283
Location
Toronto , Ontario
OP
THe plug that you found is fine for your application
The rating 3 HP phase rating means that the plug is capable of 3 HP per phase for 9 HP total
Your 7.5 HP 3 ph motor rating will draw approx 20 amps at full load Amps
According to charts. Check the nameplate rating on your motor
Therefore a 30 amp plug will be fine
We used this approach in our factory all the time
Direct wiring is always better of course

https://www.hubbell.com/wiringdevic...geRatingDescription:3+Phase+WYE+120%2F208+VAC

I assume that you have a 208 v 3 ph system which is very common
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,054
Location
Modesto, CA
OP
THe plug that you found is fine for your application
The rating 3 HP phase rating means that the plug is capable of 3 HP per phase for 9 HP total
Your 7.5 HP 3 ph motor rating will draw approx 20 amps at full load Amps
According to charts. Check the nameplate rating on your motor
Therefore a 30 amp plug will be fine
We used this approach in our factory all the time
Direct wiring is always better of course

https://www.hubbell.com/wiringdevic...geRatingDescription:3+Phase+WYE+120%2F208+VAC

I assume that you have a 208 v 3 ph system which is very common

Most of the plugs and receptacles on your link are either non-grounding 120/208Y or 5-wire.

OP only need 4-wire grounded
 

Lightning rod

Well-known member
Joined
Dec 1, 2012
Messages
283
Location
Toronto , Ontario
WD
I did peruse the “PHASE TECHNOLOGIES” website but honestly didn’t open a manual to see details
I should have been more clear in my post in that the webpage illustrated what I used in the factory testlab
If the converter needs just 3 phases and a ground , then 4 wire grounded would be correct
If the converter needs a neutral, then 5 wire would be needed
Maybe the OP can give more detail on his model for a more precise answer
In any event, plugs and sockets can be had for what he is trying to do.
Thanks for the input
 