Timer on/off switch for 220v?

ilikedirt

Well-known member
Joined
Dec 27, 2014
Messages
162
Location
Northern VA
Question, I have a Profusion 7500w shop heater and I want to keep the shop around 50 degrees. It does such a good job even turned all the way down it keeps it a lot warmer than what I need it. So i'd like to put it on a timer or some sort of thermostat to save some electric $..

Anyone have an ideas?
 
To avoid these ads, REGISTER NOW!

C96

Well-known member
Joined
Nov 30, 2013
Messages
1,251
I thought those came with a thermostat to control the temperature…:headscrat
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
2-pole Intermatic time switch with a 208-277V timer motor would do well. BTW, 220V is a obsolete voltage not used in the US since before WW II, 240V is the standard today.
 
OP
I

ilikedirt

Well-known member
Joined
Dec 27, 2014
Messages
162
Location
Northern VA
2-pole Intermatic time switch with a 208-277V timer motor would do well. BTW, 220V is a obsolete voltage not used in the US since before WW II, 240V is the standard today.

Sweet, I will look for one of those..

Whoops! Shows my electrical expertise :lol:
 
OP
I

ilikedirt

Well-known member
Joined
Dec 27, 2014
Messages
162
Location
Northern VA
I found the timers at HD the other day. I'm thinking now I want to put it on a thermostat to where I can control exactly what temperature i'd like it to cut off at. Anyone put an auxiliary on one of these?
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The problem you'll have is finding a line voltage thermostat that's rated to work on a 7500W heater. You'll most likely need to use a contactor controlled by a 24V thermostat.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
The problem you'll have is finding a line voltage thermostat that's rated to work on a 7500W heater. You'll most likely need to use a contactor controlled by a 24V thermostat.


How about a contactor with a 240V coil, run directly from the line voltage thermostat?

The highest amp rated thermostat I've been able to find is 22A, the heater draws 31.25A so it would definitely need a contactor to do it that way in any case.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
How about a contactor with a 240V coil, run directly from the line voltage thermostat?

The highest amp rated thermostat I've been able to find is 22A, the heater draws 31.25A so it would definitely need a contactor to do it that way in any case.

Yep.. I didn't think of a contactor with a 240V coil.
 