To junction or not

onlyn8v

Well-known member
Joined
Nov 27, 2010
Messages
85
Location
Terryville NY
I pulled 2/2/2/4 for 100 amp to my garage

I now have to get into my panel. If I go below my panel with an lb outside, can I run a junction box for purpose of making the 90 bend to my panel using pvc sch. 40 and cover it up? I know youre not allowed to cover for splices, but is it the same rule?

If yes, what else could I do?

Thanks
 
To avoid these ads, REGISTER NOW!

7635tools

Well-known member
Joined
Feb 19, 2015
Messages
87
Location
Southeast Wisconsin
If you mean cover the junction box with drywall, plywood, etc., then no. It would not be code compliant to bury a box whether the cables are spliced or not.


Sent from my iPhone using Tapatalk
 

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,919
Location
Southern Oregon
You can put an access panel over it, either a removable drywall panel, or a something premade.
 

Attachments

  • whites-access-panels-34056-64_1000.jpg
    whites-access-panels-34056-64_1000.jpg
    30 KB · Views: 34

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,647
Location
BC
You could also go up the outside wall a little further and come straight into the back of the panel.
 
OP
O

onlyn8v

Well-known member
Joined
Nov 27, 2010
Messages
85
Location
Terryville NY
I assume you are aware that if the 2-2-2-4 is aluminum it's not rated at 100A. It's 90A.

Honestly, no.

All the ampacity charts I looked at said xhhw2 #2 was rated at 100. I tried to do all the research I could but, not having an nec book its easy to screw up.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Terminals are rated at a max of 75deg.C so that limits the max temp of the feeder. 90deg.C is used when derating.
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
you could put in two LBs...one outside, one inside. Then pop in a double gang low voltage ring and double plate.

media.nl

You need to be able to 'access' the cover. Not that you will actually every need to use it. Ever.



Oh, dont sweat the 10 amps. (90 vs 100) You will never need it. ;)



.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,258
Location
Modesto, CA
Honestly, no.

All the ampacity charts I looked at said xhhw2 #2 was rated at 100. I tried to do all the research I could but, not having an nec book its easy to screw up.

The NEC code books are available online for free.

Go to nfpa.org and make an account

#2 al is most definitely 90a NOT 100a.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,368
Location
Coronado, CA
The NEC code books are available online for free.

Go to nfpa.org and make an account

#2 al is most definitely 90a NOT 100a.

Now that you have been given knowledge, you now know an answer; but understanding the knowledge you have been given is not automatic.
 

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,919
Location
Southern Oregon
Maybe this handy chart will help, or not.
Excerpt from NEC 2017 ampacity table.
#2 AL XHHW-2 falls in the 90C column (100A) for derating purposes, but drops back to the 75C column (90A) for practical purposes as stated above.
 

Attachments

  • nec-2017-153.JPG
    nec-2017-153.JPG
    64.2 KB · Views: 34
OP
O

onlyn8v

Well-known member
Joined
Nov 27, 2010
Messages
85
Location
Terryville NY
Maybe this handy chart will help, or not.
Excerpt from NEC 2017 ampacity table.
#2 AL XHHW-2 falls in the 90C column (100A) for derating purposes, but drops back to the 75C column (90A) for practical purposes as stated above.

I knew I saw it! But, I had no idea about terminals.

I will be having the panel in the home uprated to 200 and I was not sure it I get as much done as possible before the install, but I should be able to come right through the back of the panel with an LB so, for now should be ok
 
OP
O

onlyn8v

Well-known member
Joined
Nov 27, 2010
Messages
85
Location
Terryville NY
Electrician came out, did the 200amp upgrade and I finished the connection to the new panel.
Now, onto the wiring in the new garage
 