Do I just run two stretches of 6-2 romex to the outlet?

black on one power, black on the other power, both whites to one pole and both greens on the other... And then the same in the box.

Do I have it right?
 
To avoid these ads, REGISTER NOW!

79pacecar

Well-known member
Joined
Jun 19, 2009
Messages
90
Location
Wisconsin
Just run 1 6/3 (Assuming #6 is big enough)
Black = Hot
Red = Hot
White = Neutral
Bare = Ground
 

lametec

Well-known member
Joined
May 5, 2008
Messages
2,099
Location
Michigan
Or, if the outlet you're wiring up doesn't use neutral, just use your 6-2, wire black and white to the two hots, green/uncovered to ground. Wrap the white wire with red electrical tape at the outlet and in the breaker box so as to identify it as a hot wire.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
if its for a welder, compressor, or some other device which uses a 3 pole receptacle, you only need 6/2(with ground). Reidentify the white wire with black or red tape. You can never run 2 cables with one hot (or any other part of the circuit for that matter) in another cable.
 
To avoid these ads, REGISTER NOW!
OP
V

v7guy

Well-known member
Joined
Jun 7, 2009
Messages
557
Location
Hudson valley, NY
if its for a welder, compressor, or some other device which uses a 3 pole receptacle, you only need 6/2(with ground). Reidentify the white wire with black or red tape. You can never run 2 cables with one hot (or any other part of the circuit for that matter) in another cable.

Is this a common wiring method?

I can't seem to find any info on this and the guy that's helping me has said he's never heard of wiring it this way (he's not an electrician either though). I want to do it "right" but I'd hate to throw away $150 of wire. Thanks for humoring me guys
 
Last edited:

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
Is this a common wiring method?

I can't seem to find any info on this and the guy that's helping me has said he's never heard of wiring it this way (he's not an electrician either though). I want to do it "right" but I'd hate to throw away $150 of wire. Thanks for humoring me guys

is what a common way, using the white for your other hot? Thats the way its done......you only need 6/3 (red, black, white, ground) if you are installing a 4 wire receptacle which provides 120/240. These are most commonly used on ranges and larger RVs.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Code allows you to use the white wire in a cable and remark the exposed ends as a un-grounded (hot) conductor. You would not be allowed to do this with loose wires pulled in a conduit however.

If that aspect of it is what you are wondering is common, yes, it is.