I have an ultrasonic cleaner that is designed for 220/240 VAC and 1.75A. I'd like to be able to use plug it in 120V outlets. The step up transformers I find have european style outlets. What other options do I have?
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,775
Location
NW Iowa
Probably not going to find anything premade with plugs. A 120x240 500VA transformer would be easy to find though.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Look for "travel transformers", most will be to allow 120V appliances to operate on 240V, but they are out there, no need to reinvent the wheel.

 
Last edited:

Lassen Forge

Well-known member
Joined
Apr 26, 2014
Messages
15,391
Location
The romantic hills of central Umbria, Italy,
It's more than just volts - EU 230 volt systems run on 50 Hz... 120V us runs on 60Hz. Most things that is designed to run on one that have computer controls will not function well (if at all) on the other. I just spent a small fortune on a "power exchanger" that changes 120V60Hz to 230V50Hz so I can run my US standard stuff I can't get in the EU there...
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,870
Location
Richmond, VA
It's more than just volts - EU 230 volt systems run on 50 Hz... 120V us runs on 60Hz. Most things that is designed to run on one that have computer controls will not function well (if at all) on the other. I just spent a small fortune on a "power exchanger" that changes 120V60Hz to 230V50Hz so I can run my US standard stuff I can't get in the EU there...
That's why I asked for the nameplate, which shows 240v 60hz. Just needs to up the voltage, or put in a 240v receptacle and change the cord end
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,313
Location
Dutzow Missouri
When I have used the travel transformers the wattage /power rating on the box are a joke and must be derated by 5X if you plan on operating the equipment at its rated voltage.

Shop by looking at the shipping weight 1 pound is good for 25VA so any transformer under 20 pounds is likely a waste of time and money.

Walta
 
OP
L

Leaflessshadetree

Well-known member
Joined
Aug 1, 2013
Messages
7,175
Location
Don't ask.
what kinda plug is on the end of the cleaner?


cause this has a universal recep for the 220.
I have a NEMA 6-20P on it but it is not original. I'm not familiar with "universal" 220 but looking at the image it looks similar to some of the plugs with round pins used in Europe and elsewhere. I'm guessing that a NEMA 6-20 (or maybe 6-15) could fit but don't know how well they would work.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
It's more than just volts - EU 230 volt systems run on 50 Hz... 120V us runs on 60Hz. Most things that is designed to run on one that have computer controls will not function well (if at all) on the other. I just spent a small fortune on a "power exchanger" that changes 120V60Hz to 230V50Hz so I can run my US standard stuff I can't get in the EU there...
Better go look at the nameplate he posted.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
It's more than just volts - EU 230 volt systems run on 50 Hz... 120V us runs on 60Hz. Most things that is designed to run on one that have computer controls will not function well (if at all) on the other. I just spent a small fortune on a "power exchanger" that changes 120V60Hz to 230V50Hz so I can run my US standard stuff I can't get in the EU there...
Transformers do not change frequency, only voltage up or down, changing frequency is expensive.
 

Steve from Socal

Well-known member
Joined
Jan 27, 2009
Messages
3,510
Location
Hutchinson Ks.
The device IS dual rated 220/50 and 240/60.

As Bert mentioned just get a 240/120 and run it in reverse. Maybe wire the transformer so it is on when plugged in and the on/off is on the 240 side.

Steve
 
To avoid these ads, REGISTER NOW!

Phantomd

Well-known member
Joined
Aug 26, 2015
Messages
183
Location
Near Boulder CO
Are you sure a NEMA 6-15 wont work?
The model number is US-**** - I would bet the manufacturer made that model for the US market.
There are a few 220v 60hz contries, but every piece of equipment that ive seen with a 60hz rating with a tag in english is made to run on 2-pole (single phase) 250v which is common in the US.

I am unable to find any info on that model number of ultrasonic cleaner.

Can't tell you how many times I've seen excessive voltage changes with transformers and such when the equipment does not really care.
 

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
I read the tag as:
220 / 240 volts 50 / 60 hz
I have always interpreted as 220 v / 50 hz or 240v / 60hz
 
Last edited:
OP
L

Leaflessshadetree

Well-known member
Joined
Aug 1, 2013
Messages
7,175
Location
Don't ask.
Are you sure a NEMA 6-15 wont work?
The model number is US-**** - I would bet the manufacturer made that model for the US market.
There are a few 220v 60hz contries, but every piece of equipment that ive seen with a 60hz rating with a tag in english is made to run on 2-pole (single phase) 250v which is common in the US.

I am unable to find any info on that model number of ultrasonic cleaner.

Can't tell you how many times I've seen excessive voltage changes with transformers and such when the equipment does not really care.
The unit works fine at 240V and 60Hz (just like the tag says). I don't plan on taking it to other countries but I expect it would work at 50Hz and 220 or 230 V though maybe some minor difference in vibration or heating performance.
Yes a 6-15 would work if I installed a 6-15 receptacle. I don't see where that is any different than the 6-20 I have now.

The travel transformer appears to be the lowest cost option. I ordered one rated at 1000W.
 

Lassen Forge

Well-known member
Joined
Apr 26, 2014
Messages
15,391
Location
The romantic hills of central Umbria, Italy,
I have a few devices that need that (damned) 60Hz to work right - and there's not a real good alternative in the EU. Otherwise I'd just use a transformer and deal with the frequency difference... But even something like my Miller 211 that WILL run (quite well) on 230 still needs that (deleted) 60 Hz... The 5% difference between 220 and 240 is negligable (our "230" house current in Italy tests consistantly over 240) and were it not for that... well... yeah.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,048
I read the tag as:
220 / 240 volts 50 / 60 hz
I have always interpreted as 220 v / 50 hz or 240v / 60hz
You're right if it's a motor - mostly. Hz determines RPM. if so, they generally list the RPM at the frequency.

anything with a SMPS inside dgaf about the frequency, and barely cares about the voltage.
or a universal motor - those used to come name-plated for DC-60Hz, or 0-60Hz too.

with something like this, there's a lot they're leaving out.
1640314734870.png

this one is more honest:
1640314770033.png
47Hz at 100V, 63Hz at 250V, right?

and then there's this one that pulls 820W to put out 330W. :ROFLMAO:

1640314814111.png


or this one that can run at 200V, or on a 277V lighting circut, but you better get the frequency right for the voltage, or else!
1640315002688.png


Lesson #B: all nameplates are lies. unless it's a synchronous motored clock. I never understood how 50Hz countries can think 50Hz makes sense with 60 seconds in a minute!
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
You're right if it's a motor - mostly. Hz determines RPM. if so, they generally list the RPM at the frequency.

anything with a SMPS inside dgaf about the frequency, and barely cares about the voltage.
or a universal motor - those used to come name-plated for DC-60Hz, or 0-60Hz too.

with something like this, there's a lot they're leaving out.
1640314734870.png

this one is more honest:
1640314770033.png
47Hz at 100V, 63Hz at 250V, right?

and then there's this one that pulls 820W to put out 330W. :ROFLMAO:

1640314814111.png


or this one that can run at 200V, or on a 277V lighting circut, but you better get the frequency right for the voltage, or else!
1640315002688.png


Lesson #B: all nameplates are lies. unless it's a synchronous motored clock. I never understood how 50Hz countries can think 50Hz makes sense with 60 seconds in a minute!
Tesla preferred 60 hertz, but 50 hertz is "metric".
 

BukitCase

Well-known member
Joined
Apr 11, 2017
Messages
1,075
Location
Oregon
Lassen -

"even something like my Miller 211 that WILL run (quite well) on 230 still needs that (deleted) 60 Hz"

Depends - is your mm211 the older transformer model, or the newer inverter? If it's the transformer one, then yeah; 60 hZ ONLY.

The inverter version is OK with either frequency. From the inverter 211 manual, section 4 -

"Amperes Input at Rated
Load Output,
50/60HZ, Single−Phase "


I verified this with a call to Miller tech support. Several years ago my first mig was a transformer mm211, I later found a mm252 with NIB 30A spool gun, dual running gear, 3 bottles, for less than HALF the new price; so I sold the ****** 211 to a friend (he got as good a deal as I did), then decided I wanted to add a smaller unit for an "offroad" version so I bought the inverter 211.

The "offroad" cart I built for the inverter 211

Only reason I cared about the frequency is my 8 k genny tends to wander off frequency a little, and I didn't want that to be a concern... Steve
 
Last edited:

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
Lesson #B: all nameplates are lies. unless it's a synchronous motored clock. I never understood how 50Hz countries can think 50Hz makes sense with 60 seconds in a minute!
Lol!
thanks for the illustrations - those are great to show the different name plates and the nuances they present. The show that it is device dependent. Just shows you how much we forget as we age👴
I would read the first one a little different. The 100-240~, 50/60hz I would read "voltage from 100v to 240v (because of the ~ "tilde") at either 50 or 60 hz. Also, power supplies (switching mode) really are loose because of their conversion to DC and internal regulation. The others are just plain mean.
 
Last edited:

htmdude57

Well-known member
Joined
Apr 28, 2014
Messages
173
Location
Hudson Valley, New York
It might be that if you opened up the ultrasonic unit, you might find that it has a transformer inside that drops the input voltage down to something like 12 or 24 volts to run the electronics. If so, you could replace the internal transformer?
 

Solarphil

Well-known member
Joined
Mar 21, 2017
Messages
47
Yes a 6-15 would work if I installed a 6-15 receptacle. I don't see where that is any different than the 6-20 I have now.

You are correct - the 6-20 would be perfectly fine for your application. It will have a little more theoretical ’headroom’ than you need for your application, but no worries there since you already own it. The travel transformer will be the limiting factor in the power chain.

As someone who’s built power systems for multiple countries, I’ve found 220 / 240 nomenclature to be more slang than actual definitions of a voltage standard available at any one given receptacle across this world - there’s just too much variation in voltage at different points in the line across different regions, even within one country. However what’s clear is this particular device doesn’t GAF what frequency it’s fed, and will draw 1.75 Amps when fed 220 volts, perhaps a bit less when fed 240.
 
OP
L

Leaflessshadetree

Well-known member
Joined
Aug 1, 2013
Messages
7,175
Location
Don't ask.
The travel transformer works.
That "universal" receptacle accepts many types of plugs including NEMA 6-20 and 6-15.
I'm a bit surprised this is available because allows 120V plugs {5-15 or 520) to be connected but the voltage is 240V.
 