transformer with two primaries ?

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
I have this transformer laying around that have two primaries and one secondary... can some one explain that to me how it works or what was the purpose of that 2nd primary?
Can I repurposed it to be a secondary for 1:1 isolation output ?

transformer is Toroidal 375VA with 2 110v primary and 24V secondary...


Normally I would only see a 2 lead primary or multiple tap primary.... but this one seems to have two individual primaries... .. weird.
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,929
Location
NW Iowa
120/240 V primary?

Transformers over a few hundred VA usually do not use taps for different voltages. Unless it is just to make small changes like a couple volts.
 

htmdude57

Well-known member
Joined
Apr 28, 2014
Messages
175
Location
Hudson Valley, New York
There's 2 things I can think of: it could be a dual input voltage transformer that can be wired with both primaries in parallel to handle 120V in, or wired in series to handle 240V in.
Or, it could be an isolation transformer, so that the second 120V winding is an output. These are sometimes used in medical equipment to make it so that the equipment is not running on grid. It is safer for the user.
Actually, any transformer can work both of the above ways.
 
OP
D

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
doorbell circuit at the embassy? Their power/network vs ours?

LMFAO...\but haven't you heard, Embassay's don't use door bells .. they save those transformers for shock treatments :)

Na... have a 115Vdc 1/10hp gear motor I would like to use by adding a bridge rectifier and a capacitor..if I can use that other primary as secondary... not too sure how these Toridal transformers works.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
11,179
Location
Rhode Island
Transformers don't care. A winding being a "primary" or a "secondary" is just a label we put on it. You could feed 24vAC into the "secondary", and it would then become the primary.

As others mentioned, it's likely configured so that you'd run both primaries in parallel for 120v operation, and in series for 240v operation. You could hook up one primary, and then use the other as an isolated 120vAC secondary if you wanted. The only issue is you'd lose half the capacity of the transformer.
 
OP
D

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
Are you sure its 2 primaries?

Post a pic of the wiring diagram

Yea at least on the label it is Most of the other toroidal transformer of this kind that I have are straight forward 120V primary and 24V secondary some with extra secondary taps for what other voltage stuff... but only this one listed 2 primary... Maybe it is for 120/240 thing... will test.. just thought I would ask first, maybe someone is familiar, I do remember there are few people here that are transformer experts here... some time back, don't know if they are still here... per se...

pic attached...




I would love to build a 1000VA one like this guy but finding those raw materials here would probably cost the first born.

 

Attachments

  • toroidal1.JPG
    toroidal1.JPG
    91.9 KB · Views: 77
  • toroidal2.JPG
    toroidal2.JPG
    111 KB · Views: 57
Last edited:

Sevenhills1952

Well-known member
Joined
Aug 30, 2018
Messages
1,750
Location
Virginia
LMFAO...\but haven't you heard, Embassay's don't use door bells .. they save those transformers for shock treatments :)

Na... have a 115Vdc 1/10hp gear motor I would like to use by adding a bridge rectifier and a capacitor..if I can use that other primary as secondary... not too sure how these Toridal transformers works.
As others say, dual primary is for 120 or 240v in. That 115 VDC motor you wouldn't want to run off of 120 VAC with bridge and capacitor. Reason is DC output will be about 169 VDC. You would either need a regulator, 169vdc in, 115vdc out or a transformer with 120vac primary, 83v~ secondary.

Sent from my SM-S320VL using Tapatalk
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,929
Location
NW Iowa
Kink of strange they don't give you a diagram or something. If it is a 120/240 primary you would have to figure out what color goes to each winding and figure out the phasing.
 

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,933
Location
oregon
Kink of strange they don't give you a diagram or something. If it is a 120/240 primary you would have to figure out what color goes to each winding and figure out the phasing.

Not if it is a machine specific part. Common to have 120/240 machines where just connect to a listed set of terminals. Inside the machine the wiring is done to use the correct inputs to get the 24v out for control wiring.

lg
no neat sig line
 
To avoid these ads, REGISTER NOW!

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Wire the two primaries in series....and you can hook it up to 240 Vac

Wire them in parallel.....you run it off 120

Or

Wire the two primaries in series...connect to 120Vac......and you get 12 Vac out....

But....you need to know the terminal #'s..

The primary side should be something like H1, H2, H3, H4....typically, you would tie H2 and H3 together for series operation. And 'typically', for 120Vac...H1-H2 together and H3-H4 together....typically
 
OP
D

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
As others say, dual primary is for 120 or 240v in. That 115 VDC motor you wouldn't want to run off of 120 VAC with bridge and capacitor. Reason is DC output will be about 169 VDC. You would either need a regulator, 169vdc in, 115vdc out or a transformer with 120vac primary, 83v~ secondary.

Sent from my SM-S320VL using Tapatalk

yes will take into account for RMS.
 
OP
D

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
Kink of strange they don't give you a diagram or something. If it is a 120/240 primary you would have to figure out what color goes to each winding and figure out the phasing.

I think that would be harder to find out.. the phasing... it can't be done with a regular multi-meter... maybe a function generator and a scope?
 
OP
D

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
Transformers don't care. A winding being a "primary" or a "secondary" is just a label we put on it. You could feed 24vAC into the "secondary", and it would then become the primary.

As others mentioned, it's likely configured so that you'd run both primaries in parallel for 120v operation, and in series for 240v operation. You could hook up one primary, and then use the other as an isolated 120vAC secondary if you wanted. The only issue is you'd lose half the capacity of the transformer.

This is a weird one... at least different... I just don't wanted to be surprised like this guy when hooking it up... Primary/Secondary is not interchangeable... but this one listed 2 primary and it's a Toroidal transformer instead of a E-I core... that I don't know...

 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,929
Location
NW Iowa
I think that would be harder to find out.. the phasing... it can't be done with a regular multi-meter... maybe a function generator and a scope?

Connect one winding to 120 then measure between one lead of the unconnected winding and the one you are powering. Leads that have 0 volts between them would go together for 120v operation.
 

FordTruckWench

Well-known member
Joined
Jan 8, 2015
Messages
539
Location
California
Connect one winding to 120 then measure between one lead of the unconnected winding and the one you are powering. Leads that have 0 volts between them would go together for 120v operation.

Won't work, you have to connect one lead of the "alternate" primary before you can measure anything. With the alternate floating, you'll read zero volts no matter the end - or actually, if your meter has high enough input impedance, you might read 60VAC due to leakage.

So: Connect neutral to one lead of both primaries. Connect hot to the remaining lead of one primary. Now measure between hot and the remaining primary lead. If you measure 0VAC, then the neutral is connected properly and you can just connect the last lead to hot. If you measure 240VAC, then you need to "flip" the second primary.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,929
Location
NW Iowa
Won't work, you have to connect one lead of the "alternate" primary before you can measure anything. With the alternate floating, you'll read zero volts no matter the end - or actually, if your meter has high enough input impedance, you might read 60VAC due to leakage.

So: Connect neutral to one lead of both primaries. Connect hot to the remaining lead of one primary. Now measure between hot and the remaining primary lead. If you measure 0VAC, then the neutral is connected properly and you can just connect the last lead to hot. If you measure 240VAC, then you need to "flip" the second primary.

Your right. I didn't think that through well enough.
 

Sevenhills1952

Well-known member
Joined
Aug 30, 2018
Messages
1,750
Location
Virginia
First, an ohm meter will give you an idea of the windings. An unknown transformer if two leads are, say, 50 ohms and two are 5 ohms you know 50 is the primary, 5 is secondary and about 10:1 ratio.
Here's a tester you can make, I use it all the time. You need a lamp base, 7W lamp, 6ft. lamp cord, two alligator clips.
The narrow a.c. cord plug spade is hot, cut this lead a foot or so from plug...series in light socket, then to an alligator clip. Wide neutral alligator clip on end.
Be careful when using...but it's basically shock proof (7 watt bulb).
Shown...I'm touching the leads.
Shorting clips together lights the light.
It's a simple $5 current limited supply.
You can check transformers perfectly because the 120V goes through the light. Using higher wattage lamp=more current.
Accidentally connect to secondary does no harm...light will be bright. Primary you can measure output voltage, light will be dim.
I keep one over work benches to test fuses, lights, even automotive, etc.
2109d44647ef8011988abbdf67535625.jpg
4b2d8de84cb19bf81dbc939cd5b31895.jpg
42e706cb76b372e84ddf3b9ffc6c3df8.jpg
bdaf6d467013f86f531cfea1ae964a72.jpg
light.jpg

Sent from my SM-S320VL using Tapatalk
 
OP
D

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
hmmm thx that is a great idea...to use bulb as current limiting...

Well, will test all the suggestions folks, right after the turkey digested :) Not sure why my eyes can't keep wide open after the turkey.

Thx folks... Happy Turkey Day.
 

log man

Well-known member
Joined
Dec 2, 2013
Messages
80
Location
new york state
Your tester is quite like my “cheater” but I don’t have the bulb in series. I’m a sparky and quite comfortable with it. However, I erred and let my neighbor see it and he made one. I made him promise to call me and I’d come up if he wants to use it....
 