Hi all, My new-to-me garage has a surface mount subpanel with some existing outlets ran though PVC conduit on a finished wall. I am looking to run 2 additional circuits to the unfinished walls that will require running more pvc conduit to a junction box to tie the THHN to NM that will be run through the walls that eventually will be finished.

I'd prefer to use PVC to match the existing conduit but I am struggling to find any pvc fittings for the transition of NM into the PVC junction box.

Any guidance is appreciated.

Sent from my SM-G935V using Tapatalk
 
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,503
Location
Minneapolis
NM usually means non-metallic conduit, which would be PVC...are you referring to transitioning to flexible conduit?
 
OP
G

Grahams315

New member
Joined
Aug 19, 2018
Messages
4
Location
New york
Apologies, I'm referring to NM cable or Romex. One the hard pvc conduit gets to the unfinished wall I'll be running romex through the studs to each box.

Sent from my SM-G935V using Tapatalk
 
To avoid these ads, REGISTER NOW!

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
Couple of different ways:
1. Run PVC conduit to a metal junction box with knockouts, use a regular 2-screw cable clamp for the NM cable. Connect a bonding jumper to the metal box

2. Install a PVC box that has knockouts and install a 2-screw cable clamp with a bonding locknut and connect a bonding jumper to it.

3. Install a PVC box that has knockouts and install a plastic "button" type cable clamp

4. Install a PVC box that has the "trap doors" for sliding NM through instead of knockouts. Drill a hole in the box (make your own knockout) for the conduit.
 
OP
G

Grahams315

New member
Joined
Aug 19, 2018
Messages
4
Location
New york
Couple of different ways:
1. Run PVC conduit to a metal junction box with knockouts, use a regular 2-screw cable clamp for the NM cable. Connect a bonding jumper to the metal box

2. Install a PVC box that has knockouts and install a 2-screw cable clamp with a bonding locknut and connect a bonding jumper to it.

3. Install a PVC box that has knockouts and install a plastic "button" type cable clamp

4. Install a PVC box that has the "trap doors" for sliding NM through instead of knockouts. Drill a hole in the box (make your own knockout) for the conduit.
Thanks! Number 3 was what I was thinking of, but pvc boxes with knock outs seem to be harder to find than I thought. Any issues with getting a standard surface mount box and drilling my own "knock out" into it?

Sent from my SM-G935V using Tapatalk
 

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
Seems to me to u could also use a box with threaded holes, and screw an NM clamp into one of the holes. Run PVC into it with a threaded fitting. Pretty much the same as using a metal box but without the nuts.

It isn’t clear to me how you want to transition (surface mount or flush) so I can’t picture exactly how it would look for your case. I recently installed recessed receps in a brick wall with a similar concept.
 