tripping breaker

oil man

Member
Joined
Dec 4, 2009
Messages
21
what will cause an air compressor to trip the breaker only when it gets cold outside....the compressor is outside
 
To avoid these ads, REGISTER NOW!

sparky36000

Well-known member
Joined
Dec 25, 2012
Messages
116
Location
North Dakota
I think you answered your own question. It's cold and outside. If it's oil filled like mine, it has a hard time starting when it's very cold. Your breaker can handle the starting current when it's warm. But when it's cold and the motor tries to turn the stiff compressor, the starting current stays high long enough to trip the breaker.
 
To avoid these ads, REGISTER NOW!

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,877
Location
oregon
You could try focusing a lamp on the compressor to keep it warm or warm it up the night before you need to use it.

lg
no neat sig line
 

Gary S

Well-known member
Joined
Dec 27, 2008
Messages
2,972
Location
Bismarck, ND
I solved that problem with my air compressor by upsizing the wire from #12 to #10. With the larger wire, the 20A breaker no longer trips because the motor starts faster.
 
OP
O

oil man

Member
Joined
Dec 4, 2009
Messages
21
thanks guys....I have #8 wire going to it so I feel like that is big enough. Probably the oil, Im going to change is to some thinner stuff and put a light on it
 