I have a 26' x 38' x 10' garage with 2"x6" walls.Walls and ceiling insulated and 2" under floor and 1 " along outside edge. 2 8'x10' over head door and 1 service door.
I have a Navien on demand HW heater(210a)17000-17500btu that I hooked up to the infloor system(temp/pressure gauges, pressure tank, air elimanator, pressure relief safety valve,pump) and I am having trouble getting a delta t of 20 degrees.
I had temp going out @ 120 and coming back @ 65. Called plumber and thought air in system or to small of a pump. Circulated each line(4 250') 15 minuted to get air out,still low temp coming back and heater seems to be starving for more flow(stays on low heating cycle).
Replaced pump(grundos ups 15-58) with stiebel eltron cp3s26-110fc running on medium speed.
Temp return now up to 75 degrees, but still cant get Delta t of 20 and seemed to take about a hour to raise Temp 1 degree.
Also heater is modulating higher since I installed bigger pump.
I did clean all filters and strainers and found some blockage.
My Questions Why such a big Delta t and why is my floor heating so slow.?How do you know all the air is out of system? Floor temp is @ 60. Thanks
The floor is @ about 60 degrees
I have a Navien on demand HW heater(210a)17000-17500btu that I hooked up to the infloor system(temp/pressure gauges, pressure tank, air elimanator, pressure relief safety valve,pump) and I am having trouble getting a delta t of 20 degrees.
I had temp going out @ 120 and coming back @ 65. Called plumber and thought air in system or to small of a pump. Circulated each line(4 250') 15 minuted to get air out,still low temp coming back and heater seems to be starving for more flow(stays on low heating cycle).
Replaced pump(grundos ups 15-58) with stiebel eltron cp3s26-110fc running on medium speed.
Temp return now up to 75 degrees, but still cant get Delta t of 20 and seemed to take about a hour to raise Temp 1 degree.
Also heater is modulating higher since I installed bigger pump.
I did clean all filters and strainers and found some blockage.
My Questions Why such a big Delta t and why is my floor heating so slow.?How do you know all the air is out of system? Floor temp is @ 60. Thanks
The floor is @ about 60 degrees