I could use your troubleshooting help before I call in the pros...
We got a shiny new double oven two years ago to replace the old one and I installed it myself. Worked great. A year and a month later, just after warranty expired, it went out after running both ovens on high. Called out repair guy and they replaced a board that is a safety shutoff if it gets to hot or something and ran great since, till this weekend. It went out again when using both ovens. It came back on, we used one oven, went out and didn’t come back on.
Service guy came out today and said it was the electrical feed, not the oven. I wasn’t here to see myself, but he said leg 1 was 120v, leg 2 was 0v.
I got home, opened up front of panel outside and 50% of available air space was filled with mud dobbers attached to the neutral bar, left bar and wire feeds. Turned everything off and cleaned everything out including two lizards that didn’t make it out alive. I pulled breaker out, made sure it was clean, put it back in. It seemed to firmly click in and out. Hoping that was it, I turned it back on, no joy.
Tried metering it all out. 245 on both outbound on breaker, 120 on each to neutral bar. I tried every breaker in box and all read appropriately.
I ran out of steam, so I’ll continue tomorrow. My next steps are pull the oven and make sure this guy knows how to read a meter. Then I was going to check my second panel inside garage and make sure everything is good there. (Only been here a few years, so I don’t trust the labeling on the breakers)
Anyways... if the wires at the oven don’t register 220-240, is it safe to say one of the three wires is bad in between inside the walls and I have to get someone to pull new ones?
Couple more questions...
Would a remote continuity tester be enough to test the wire for handling voltage? Or do I need something special?
For figuring out the continuity of the neutral, is there any better way than disconnecting each wire and testing individually? (I have doubts that the position on the neutral bar corresponds with where the breaker is.
Is there anything you recomend for cleaning the panel and bars from the dirt and **** that has accumulated in the outside panel?
Thanks
We got a shiny new double oven two years ago to replace the old one and I installed it myself. Worked great. A year and a month later, just after warranty expired, it went out after running both ovens on high. Called out repair guy and they replaced a board that is a safety shutoff if it gets to hot or something and ran great since, till this weekend. It went out again when using both ovens. It came back on, we used one oven, went out and didn’t come back on.
Service guy came out today and said it was the electrical feed, not the oven. I wasn’t here to see myself, but he said leg 1 was 120v, leg 2 was 0v.
I got home, opened up front of panel outside and 50% of available air space was filled with mud dobbers attached to the neutral bar, left bar and wire feeds. Turned everything off and cleaned everything out including two lizards that didn’t make it out alive. I pulled breaker out, made sure it was clean, put it back in. It seemed to firmly click in and out. Hoping that was it, I turned it back on, no joy.
Tried metering it all out. 245 on both outbound on breaker, 120 on each to neutral bar. I tried every breaker in box and all read appropriately.
I ran out of steam, so I’ll continue tomorrow. My next steps are pull the oven and make sure this guy knows how to read a meter. Then I was going to check my second panel inside garage and make sure everything is good there. (Only been here a few years, so I don’t trust the labeling on the breakers)
Anyways... if the wires at the oven don’t register 220-240, is it safe to say one of the three wires is bad in between inside the walls and I have to get someone to pull new ones?
Couple more questions...
Would a remote continuity tester be enough to test the wire for handling voltage? Or do I need something special?
For figuring out the continuity of the neutral, is there any better way than disconnecting each wire and testing individually? (I have doubts that the position on the neutral bar corresponds with where the breaker is.
Is there anything you recomend for cleaning the panel and bars from the dirt and **** that has accumulated in the outside panel?