Two circuits on one double receptacle?

NightSky

Well-known member
Joined
Jun 29, 2024
Messages
525
Location
Southwest OH
You don't have 2 phase, 2 phase does exist in certain areas but is extremely obsolete.
I see... ChatGPT pulled me aside and explained that "2 phase" is industry terminology for old technology where the generating plant produced two phases 90 deg apart.
 
To avoid these ads, REGISTER NOW!

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,886
Never seen that in any kitchen I've been in
It was required by Canadian code for a long time, I’ve been told here.

I’ve seen it in the us, but that was in a EE’s kitchen, so it’s entirely possible he did it himself. He certainly did the 30a 240 counter top outlet. (For a proper electric kettle.).
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,391
Location
VT
It was required by Canadian code for a long time, I’ve been told here.

I’ve seen it in the us, but that was in a EE’s kitchen, so it’s entirely possible he did it himself. He certainly did the 30a 240 counter top outlet. (For a proper electric kettle.).
Not sure if I've ever been in a Canadian kitchen, maybe that's why
 

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,827
Location
Niagara Region, Ontario, Canada
Never seen that in any kitchen I've been in
"splits " was the common Canadian term and used in all kitchen outlets that were serving countertops , tables, islands etc (anything other than dedicated fridge, built in microwace etc_) . that changed when we adopted GFCI and the circuits are now 20 amp. but the splits was actually a better set up in my opinion , because you would never blow a circuit by overloading it whereas with a 20 amp, it is easily done
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,391
Location
VT
"splits " was the common Canadian term and used in all kitchen outlets that were serving countertops , tables, islands etc (anything other than dedicated fridge, built in microwace etc_) . that changed when we adopted GFCI and the circuits are now 20 amp. but the splits was actually a better set up in my opinion , because you would never blow a circuit by overloading it whereas with a 20 amp, it is easily done

Interesting.

Haven't been in many Canadian kitchens!
 

bronc076

Well-known member
Joined
Jul 17, 2023
Messages
190
Location
Ozarks
After our kitchen remodel a couple years ago I could no longer use a GFCI outlet in our island as the first receptacle in that circuit was now in the appliance garage for the microwave, and the 2nd outlet on the end of the island. My local box store only had a 15A Eaton type CH GFCI breaker in stock the day I was doing this. The wiring was all #12, I figured it would be fine as there were only two outlets.

Fast forward a couple months, my lady has the electric griddle going on the island cooking up some pancakes, and tosses some sausage in the microwave and click, the breaker trips. Testing with my amp clamp that microwave draws 10A and the griddle draws 8A. So off to the electrical supply house to get the correct 20A GFCI breaker and all is well.

Some appliances are hungry!
 

micromind

Well-known member
Joined
Sep 24, 2023
Messages
3,019
Location
Fernley, Nevada, about 30 miles east of Reno.
After our kitchen remodel a couple years ago I could no longer use a GFCI outlet in our island as the first receptacle in that circuit was now in the appliance garage for the microwave, and the 2nd outlet on the end of the island. My local box store only had a 15A Eaton type CH GFCI breaker in stock the day I was doing this. The wiring was all #12, I figured it would be fine as there were only two outlets.

Fast forward a couple months, my lady has the electric griddle going on the island cooking up some pancakes, and tosses some sausage in the microwave and click, the breaker trips. Testing with my amp clamp that microwave draws 10A and the griddle draws 8A. So off to the electrical supply house to get the correct 20A GFCI breaker and all is well.

Some appliances are hungry!

This is why code requires kitchen outlets to be on 20 amp circuits.
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,967
Location
Central Iowa
I built a house in 2006 and went overboard in the kitchen: 11 countertop receptacles, each one being it's own 20 amp circuit. Add the dishwasher/disposal, microwave, and fridge and it was up to 14 total. All I ever plugged in was a knife sharpener and occasionally a griddle for pancakes. Fast forward 1-1/2 years and I got married, she came from a farmhouse where it was a **** shoot whether the coffee pot would work without tripping. My dumb *** told her that will no longer be an issue, I had it fool proofed. I came home one night to her apologizing because she'd broken something and "nothing" in the kitchen worked. I walked in and saw the coffee pot and toaster plugged into the same outlet. The other 10 circuits were fine, she just didn't try them. After explaining what happened to her, she called me out on having it foolproofed. I told her it was foolproofed, but to idiot proof it would be next to impossible. I don't remember much of the rest of the evening.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,872
Location
NJ
Change each to single recepts! :lol_hitti Then you can go back and tell of your accomplishment. Dare ya!!!
 
Last edited:

bronc076

Well-known member
Joined
Jul 17, 2023
Messages
190
Location
Ozarks
Eaton type CH in a cutler hammer panel. We don't all use ****.

I tested current draw with an amp clamp, microwave pulls 10 amps, griddle pulls 8. I didn't check the wok.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,886
I doubt a 20a breaker wouldve held with a microwave and griddle running at the same time...
Short excursions above 20a aren’t going to trip most breakers. So even if his appliances are just over 20a, I doubt he will have nuisance tripping.

A QO or HOM 20a breaker will supply 30a for at least 30 seconds and perhaps as long as 120 seconds before it trips, depending on lots of factors. That’s according to Schneider’s trip curve; the nema standard allows twice the rated current for 6 or 7 minutes. The magnetic trip isn’t hit until about 10 times current. (That’s all from memory, so I may be slightly off on the numbers, but that’s the general shape of the curve)
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,872
Location
NJ
18A should have held somewhere in between 1-5 min on a 15a cb. Every cb has manufacturing tolerances as indicated by the grey band.
1755305198952.png1755305271813.png
 