Two heaters combined 4500w

krisway

Well-known member
Joined
Jan 4, 2013
Messages
58
Location
Newfoundland, CA
I'm stillin the planning stages. But is it safe to run two base board heaters (one on each side of my garage) one 2000w and the other 2500w. I will be running them with 10/2 wire off a 30 amp dbl breaker. And leaving the heater on 10 degrees for the winter months.
 
To avoid these ads, REGISTER NOW!

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Yes, you are fine doing that.
#10 is a bit of a pain to work with, if breaker space is not an issue I'd run #12 (or even #14) to each one separately.
 

jvitez

Well-known member
Joined
Nov 30, 2009
Messages
2,429
Location
Big Sky Country, Canada
4500 watts divided by 240 volts equals 18.75 amps, multiplied by 1.25 for continuous load equals 23.4 amps. The next standard breaker size is 30 amps, so yup, you're fine.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,050
Location
Modesto, CA
Speedy- what's the relevant code section for the 1.25 multiplier. Finally got my NEC book and would like to know what article/code section that's in. Thx!
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,050
Location
Modesto, CA
Thx pattenp. I was gonna read that section when I realized I left my code book in my work truck so ill look tomorrow. Thx again! :thumbup:
 