Type QT breaker

thewoodster

Member
Joined
May 27, 2023
Messages
11
Backstory:

A few days ago, the power went out and came back on a few times. After that, everything seemed to be working fine, but now the outdoor ring camera doesn't work. I checked for current with a meter, and it shows current on both ends: the breaker and the actual camera. I want to replace the breaker because it seems the easiest fix. I've read that some breakers can be faulty even when current is still passing through them. So here I am, trying to replace the following.

I am looking for a Type QT breaker that feeds my 240 outlet and a 120 outdoor ring camara. I attached two images, one with the label and the actual breaker. I checked the big box, but they didn't seem to have the exact one I'm looking for, which is marked 20's on the outside and 15's on the inside. The closest one I found is this one: (https://www.homedepot.com/p/Siemens...uble-Pole-Circuit-Breaker-Q22020CT2/202315475)

Do you think that will work?
 

Attachments

  • 20250810_220135.jpg
    20250810_220135.jpg
    359.8 KB · Views: 13
  • 20250810_220634.jpg
    20250810_220634.jpg
    379.9 KB · Views: 12
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
Backstory:

A few days ago, the power went out and came back on a few times. After that, everything seemed to be working fine, but now the outdoor ring camera doesn't work. I checked for current with a meter, and it shows current on both ends: the breaker and the actual camera. I want to replace the breaker because it seems the easiest fix. I've read that some breakers can be faulty even when current is still passing through them. So here I am, trying to replace the following.
how did you test for current? current only flows if there is a load. did you mean voltage?

I am looking for a Type QT breaker that feeds my 240 outlet and a 120 outdoor ring camara. I attached two images, one with the label and the actual breaker. I checked the big box, but they didn't seem to have the exact one I'm looking for, which is marked 20's on the outside and 15's on the inside. The closest one I found is this one: (https://www.homedepot.com/p/Siemens...uble-Pole-Circuit-Breaker-Q22020CT2/202315475)

Do you think that will work?
no you need to replace like for like especially if the wire on the 15a lugs is #14. or you could go with all 15s unless the receptacles on the 20a circuit are 20a rated. home depot doesnt appear to carry the breaker you need. you could try a supply house...


 

Max

ALLIANCE MEMBER
Joined
Jun 16, 2018
Messages
3,353
Location
Georgia
I'll go one step further.

The breaker is not the problem and is a waste of money and effort.
I didn’t want to go quite that far because we don’t know if he really measured current or voltage yet. But still, if all he measured was 120V at the camera, I’d still say that the breaker was 99.9% likely to not be the issue.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,009
Location
Central Iowa
Though anything is possible, I have a hard time believing that a ring camera is the only thing on a breaker. Therefore, if everything else is working, the problem isn't the breaker. It's more likely the camera is junk, not the breaker.

Shut off the breaker that you think is for the camera and see if other things go off.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,510
Location
VT
I was surprised you didnt... Made me wonder for a sec if I was missing something
I was waiting for the OP to respond to my questions before I piled on..was clear there was probably a terminology issue at least
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,921
Location
Richmond, VA
OP
T

thewoodster

Member
Joined
May 27, 2023
Messages
11
If you have 120V at the ring camera, and if you have current flowing, then it's very unlikely that the breaker is the issue.
Thanks. I found the breaker online, so I'm going to try that first and see how it goes. Thanks again.
 
To avoid these ads, REGISTER NOW!
OP
T

thewoodster

Member
Joined
May 27, 2023
Messages
11
how did you test for current? current only flows if there is a load. did you mean voltage?


no you need to replace like for like especially if the wire on the 15a lugs is #14. or you could go with all 15s unless the receptacles on the 20a circuit are 20a rated. home depot doesnt appear to carry the breaker you need. you could try a supply house...


Thank you for pointing me in the right direction. I found it online for $52 (wow)
 
OP
T

thewoodster

Member
Joined
May 27, 2023
Messages
11
If there was a surge or brownout before/during/after the outage it may have fried or bricked the Ring camera.
That is what I am afraid of. I have two, but only one seems to be out. I am going to try the breaker 1st since it is the cheapest option. The Ring Cams have likely exceeded their warranty.
 
OP
T

thewoodster

Member
Joined
May 27, 2023
Messages
11
Even then they aren't accurate, and can give false positives (showing the wire as "hot" when it's dead)



This. Or plug something else in where the ring is (if possible) to tell
That's smart. I have the older lamp (no cam) so that might work. Thanks
 

Chuckster in NJ

Well-known member
Joined
Jan 26, 2010
Messages
2,321
Location
Hunterdon County NJ
That's not testing for current. It's testing for voltage

Get a real multi meter and actually measure what the voltage is.
It may be old but I still use this multi meter (along with Simpson 260’s) even though I have several Fluke digital meters…….. Tough to give something up that you are use to and works well as long as you care for it.
IMG_3166.jpeg
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,009
Location
Central Iowa
With a Voltage tester. (https://www.homedepot.com/p/Klein-T...ter-Pen-50-1000V-AC-NCVT1PR-NCVT1PR/317460355) When I touch the breaker on the panel, it beeps, and also when I touch the head lamp, so it seems both ends have current.
Those are referred to as idiot sticks for a reason.
That is what I am afraid of. I have two, but only one seems to be out. I am going to try the breaker 1st since it is the cheapest option. The Ring Cams have likely exceeded their warranty.
Since you have two, why not try switching them around? Changing the breaker is absurd.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,053
Location
NJ
Temporarily, move the wire to another cb.

Or plug the camera into a different circuit with an ext cord.
 

Codyboy

Well-known member
Joined
Jan 31, 2019
Messages
1,721
Location
S.E. TEXAS
So
Those are referred to as idiot sticks for a reason.

Since you have two, why not try switching them around? Changing the breaker is absurd.
Some like to throw unnecessary parts at issues when they don't understand there are protocols in troubleshooting an issue. Cars, toilets, ACs, and electrical and all the things really.
Hell, I've been on calls where someone spent 1000s on a breaker panel replacement and still have an issue.
Then finally out of desperation they'd call the POCO and I show up.
"We did this , that and still have flickering lights"
Ok I'll check it out.

Yeah, uh looks like the issue was the lug at the transformer . I made repairs.
Call back if you experience any more issues. Have a good day!

Drive off shaking my head.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
With a Voltage tester. (https://www.homedepot.com/p/Klein-T...ter-Pen-50-1000V-AC-NCVT1PR-NCVT1PR/317460355) When I touch the breaker on the panel, it beeps, and also when I touch the head lamp, so it seems both ends have current.
thats not a reliable way to test for voltage. nor is it the way to measure current, which requires a clamp meter.

that is an inductive non-touch meter. it can pickup ghost voltage from other cables nearby, giving a false positive.

get a real DMM and do an actual voltage test
 