Ufer ground with insuated slab

WisJim

Well-known member
Joined
Dec 20, 2010
Messages
2,308
Location
Menomonie, WI
My new slab has a rebar stub positioned for connection as a Ufer ground (it is part of the reinforcement of the thickened edge of the slab.) My question comes because the slab and edge has 2" of Styrofoam under it and around the perimeter, so the slab isn't in contact with the soil as required by code for use as building ground (as far as I understand it). I'm planning on putting in 2 proper ground rods and also connecting them to the rebar stub so the rebar in the slab is also connected to ground. Is this appropriate, and if not, what is recommended?
My online research of electrical sites seems to indicate that insulation between the concrete and the soil negates the use of a real Ufer ground.


(Yes, I misspelled "insulated" and can't seem to correct the thread title)
 
Last edited:
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
A couple rods won't hurt. Hook it all together. You want any steel in the place bonded and hooking to steel in the floor reduces step potential between any thing else and the floors you are standing on.
I tend to believe that pointy things driven in to the earth have to help with strikes.
 
Last edited:

Chuckster in NJ

Well-known member
Joined
Jan 26, 2010
Messages
2,321
Location
Hunterdon County NJ
A UFER ground (concrete encased >20’ long 1/2” or larger rebar) usually goes to the rebar in the concrete footing for direct earth contact...... NOT the slab. And in the OPs building having an INSULATED slab will provide no grounding.
Installing a BOND wire to the slab rebar makes the slab an equipotential plane as long as it gets connected to the electrical ground system...... A VERY GOOD system for equalizing the entire building.

Here is what I suggest: Two driven ground rods along with a footing concrete encased 20’ long rebar ground (if you have one) tied into the slab mesh or rebar...... BOND everything together!
** I know.... it’s overkill!

FACT! Proper GROUNDING and BONDING is the most important thing on an electrical system and in my opinion, you can’t over do it.
 
Last edited:
To avoid these ads, REGISTER NOW!

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,684
Location
Maine
If the slab is insulated the concrete encased rebar is not a UFER.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,056
Location
Coronado, CA
Grounding and Bonding is frequently misunderstood by many experienced Electricians.