Ufer Ground

robertearl

Well-known member
Joined
Oct 12, 2008
Messages
164
Location
Willow Park, Texas
They will be pouring the slab for my shop soon and I am working with the inspector as I will be doing my own electrical. He suggested to me to do a Ufer ground instead of driving in rods. He told me to get 20 feet of #4 stranded copper and tie it to the re-bar and turn one end up through the concrete to tie to. My question is, they are putting down a vapor barrier for the slab and I am wondering how this will work as a ground if there is a large plastic sheet insulating the slab? Is the area around the side of the slab where there is no plastic enough for the ground? I ask the inspector and he said that according to the code, it would work fine.


Reb
 
To avoid these ads, REGISTER NOW!

kbs2244

Well-known member
Joined
Nov 11, 2006
Messages
14,065
I share your doubts.
Ask him.
Maybe he didn't think about the plastic.
The idea is to get to moist dirt.
That is why the rods are 10 feet long.
 
To avoid these ads, REGISTER NOW!

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
the vapor barrier kills the ufer ground idea. the slab must be in continuous contact with the earth in order for a ufer ground to work.
 

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
if the footings are big enough it might work. you need a lot of contact area to get the proper conductance. sounds like a judgement call for the inspector.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,201
Location
Minneapolis
An Ufer ground is supposed to be in the footing anyway. Assuming your vapor barrier is only underneath the slab you should be okay.
 