I'm already going to be putting 5/8" "continuous" rebar 3" from the bottom of a footer around my to-be-poured slab.
Can I bend a piece up so that it ends above the slab at the proper location then use that for the attachment point for a Ufer ground (maybe paint the bend green to make it obvious to the inspector)?
Here's the related section of the FL code:
Can I bend a piece up so that it ends above the slab at the proper location then use that for the attachment point for a Ufer ground (maybe paint the bend green to make it obvious to the inspector)?
Here's the related section of the FL code:
E3608.1.2 Concrete-encased electrode.
A concrete-encased electrode consisting of at least 20 feet (6096 mm) of either of the following shall be considered as a grounding electrode:
1. One or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods not less than 1/2 inch (13 mm) in diameter, installed in one continuous 20-foot (6096 mm) length, or if in multiple pieces connected together by the usual steel tie wires, exothermic welding, welding, or other effective means to create a 20-foot (6096 mm) or greater length.