Well-known member
I don't have a copy of the 508A books....
But if my feeble memory serves me right, DC wires in a panel are not limited to the 14 AWG min size for AC wiring.
Translation....If I'm wiring up PLC IO cards, I can use 16 or 18 AWG wire if the ckts are DC.
For anyone who has a set of books around, it would be section 29.6 I believe.