underground conduit termination

tyme2par4

Well-known member
Joined
May 16, 2016
Messages
571
Location
NH
So I have a 8x12 outbuilding (actually a 2 story playhouse) that was built by a previous owner. It currently has 12/2 UF feeding it, but it is unprotected where it exits the ground. They also decided they would just throw a standard NEMA 5-15 plug on the end of the wire, and plug it into the exterior outlet on the house.
I'd like to fix the problems without digging up the entire 75ft run and laying conduit the whole way. Assuming the wire is buried at least 12", I believe I can run conduit from an LB on the wall down 12" to a sweep 90 on each end.

The question is, do I need something like the below on the end of the conduit? I'm guessing I'm not supposed to just leave the conduit open on the end.
I'd prefer to use PVC, as I have a couple pieces laying around already, and both ends are somewhat protected, and not subject to damage.

https://www.lowes.com/pd/Gampak-1-2-in-NM-SE-Connector/1087617
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,717
Location
NW Iowa
No connector needed, the 90 isn't needed either. I do like to run it in conduit where it exits the ground but it really only nessesary if it's subject to damage.

You don't have to follow all the rules for a normal conduit installation since this is just a sleeve.
 
OP
T

tyme2par4

Well-known member
Joined
May 16, 2016
Messages
571
Location
NH
Thanks! I've seen pictures with a gland at the end and wasn't sure if they were required.
 
To avoid these ads, REGISTER NOW!

heloc

Member
Joined
Jul 23, 2018
Messages
11
Location
Fairfax, VA
NEC Code states that UF cable should be 24" below grade or 18" below grade with a minimum of 2" concrete cover. The sleeve you want to install should extend to that depth as well to keep future owners from striking the cable while digging around the cable location.

As others have noted, the circuit should be GFCI protected as well.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
NEC Code states that UF cable should be 24" below grade or 18" below grade with a minimum of 2" concrete cover. The sleeve you want to install should extend to that depth as well to keep future owners from striking the cable while digging around the cable location.

As others have noted, the circuit should be GFCI protected as well.

If buried at 24" the circuit does not have to be GFCI protected at the source. The circuit can be buried 12" if 120V and 20A or less and is GFCI protected at the source.
 

toplessHO

Well-known member
Joined
Oct 20, 2014
Messages
14,025
Location
central florida
If buried at 24" the circuit does not have to be GFCI protected at the source. The circuit can be buried 12" if 120V and 20A or less and is GFCI protected at the source.

beat me to it
single circuit 120v exception to the burial code

I wouldnt do any substandard "feeds" to a kids playhouse.
can what ever is being powered out there be done with low voltage?
perhaps LED and solar panels,if you dont want to replace the romex
 
OP
T

tyme2par4

Well-known member
Joined
May 16, 2016
Messages
571
Location
NH
beat me to it
single circuit 120v exception to the burial code

I wouldnt do any substandard "feeds" to a kids playhouse.
can what ever is being powered out there be done with low voltage?
perhaps LED and solar panels,if you dont want to replace the romex

The only thing out there now is a single outlet and a light. Everything will be up to code as soon as I replace the plug on the end of the wire. It also has a 2 slot breaker panel in the building, so a second layer of protection.
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
That 2 slot breaker panel, does that get considered a sub panel being detached structure, with grounding rod requirements and 4 wire feed?
 