Underground from house to shop

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,014
Location
Modesto, CA
I guess, also have the 2005 NEC illustrated 3rd edition and it showed the same thing. Figured since it was the illustrated edition and not the actual NEC I would defer to you.

Might also be the thing of the word "if", that is if a subpanel does not have the ground wire coming from the main panel or is far away, that bonding and a new ground will work. Or at least that's how I read it

As Pattenp said, u need a newer code book. 3-wire feeds have NOT been allowed since NEC 2008 code cycle...BTW grounding electrodes and equipment grounding conductors are 2 different animals...

I just got done installing a panel in my new garage which is fed from a 200 amp disconnect at my barn. The local Inspector here in East TN told me to run 4 wire cable from the barn to the garage. He also told me not to install a ground rod at the garage unless "it would help me sleep at night", his exact words. Looking at your diagram it seems like I need to remedy this. I am setting myself up for trouble by not having the ground rods?

Thanks,
WAP

A ground rod is a different animal than an equipment grounding conductor. Both are required at a detached building. Grounding electrodes are for lightning strikes, to reference the voltage to ground, etc.
 
To avoid these ads, REGISTER NOW!

AllDodge

Well-known member
Joined
Feb 18, 2015
Messages
130
Location
KY
As Pattenp said, u need a newer code book. 3-wire feeds have NOT been allowed since NEC 2008 code cycle...BTW grounding electrodes and equipment grounding conductors are 2 different animals...

.

Gee thanks, I sure do appreciate your input. My last one was done around 05 and 06, so by yumpin Yemminy I'll check right into that ;)
 