My shop is in a commercial building and I have a dedicated 3 phase 208v service. (125 amp) I was looking at the day by day power breakdown from my fancy smart meter, and something isn't adding up. Looking at days where I'm not at the shop, I'm using more than 4 kilowatts.
I don't have much plugged in, and I've been checking the things I leave on with my kill-a-watt meter.
Computer - 1.58kwh/day
Fish tank - .26kwh/day
Fridge - 1.62kwh/day
That's only 3.46kwh/day. Still missing more than .5kwh! As best I can tell nothing else is on or even plugged in after I leave. My fridge is old, but my kill-a-watt says it only uses 1.62kwh/day, and that was a hot day.
Where is that extra 500 watts going? I'm starting to wonder if some of my wires aren't powering something in the neighbor's shop. (same building) Should I complain to the power company?
This is the hour by hour graph from the power company. Are those peaks my fridge kicking on and off? This is from a day where nobody was at the shop. I'm not sure what that big peak around 2AM could be? There are no lights on when I am not there, besides the fish tank. (20 watts)
I don't have much plugged in, and I've been checking the things I leave on with my kill-a-watt meter.
Computer - 1.58kwh/day
Fish tank - .26kwh/day
Fridge - 1.62kwh/day
That's only 3.46kwh/day. Still missing more than .5kwh! As best I can tell nothing else is on or even plugged in after I leave. My fridge is old, but my kill-a-watt says it only uses 1.62kwh/day, and that was a hot day.
Where is that extra 500 watts going? I'm starting to wonder if some of my wires aren't powering something in the neighbor's shop. (same building) Should I complain to the power company?
This is the hour by hour graph from the power company. Are those peaks my fridge kicking on and off? This is from a day where nobody was at the shop. I'm not sure what that big peak around 2AM could be? There are no lights on when I am not there, besides the fish tank. (20 watts)
Attachments
Last edited:
Please keep in mind the *mean average* for that period is only 228 watts RMS. You will see on the left hand side where that spike is extended.