knobby97
Member
Well I recently moved from SC to TX, and bought a home that was built in 1951 and has a detached 2 car garage about 30 feet from the main structure.
The house still has 3 phase run from the pole, even after I had the electric company change out the lines from the pole due to a bad neutral and unbalanced 120v legs. The wiring in the house was a nightmare, which I have slowly been chipping away at. Originally the mains from the meter ran into a wire gutter, where it was spliced and going to 3 panels and 2 disconnects. The house was wired with 12 awg copper with no ground. The original panel had been replaced with a 16 mini slot, main lug, GE panel. Who ever installed the panel ran it from an old 60A 3 phase disconnect box, with no high leg, and then ran 4 awg to power the panel. There were also 2 other sub panels installed on the side of the house, next to the gutter and meter, that have breakers for the pool, dryer, disposal/dishwasher, range, microwave, and an enclosed porch. There was also another old 3 phase disconnect that was powering the outside unit for the HVAC, that was wired off the 220v leg, 1 120v leg, and a neutral. Not sure why it was hooked up this way, but have since corrected it with 2 legs of 120v and a neutral. The best part is how the entire garage is run off of the kitchen lighting circuit, which is 12/2 with no ground that someone decided to put a 30a breaker on it.
I have since removed the splices in the electrical gutter, the 2 3 phase disconnects, 1 sub panel, and installed a 200a main panel next to the meter, and upgraded the wiring from the meter to the panel with #3 stranded copper. I left the 220v leg disconnect at the meter, as I don't any point to running 208v single phase to anything at the moment. The main panel currently has one old grounding rod installed and is also grounded to the cold water pipes.
So enough back ground, here is my current plan:
Everything will be moved into the 200a panel, which will feed the sub panel in the house off of a 60a breaker and another 60a sub panel to the garage.
A second copper grounding rod will be added to the main panel via 6 awg solid copper.
The wiring to the in home sub panel will be changed to 6/2 NM-B. From my understanding I will not need to run a separate ground to the in home sub panel, since the main panel is bonded and the sub panel is in the same structure.
The garage sub panel will be run with 3 x 6 awg stranded THHN and 1 x 10 awg stranded THHN for the ground. This will all be run in buried 1.25 conduit. The garage panel will not be bonded and will have its own 2 copper grounding rods on the separate bar for the grounds. The garage panel will have a 60a main disconnect (as well as the main panel), and will power 1 220v 30a plug (6 awg), 1 110v 30a plug (10 awg), interior lighting circuit (12 awg), interior outlet circuit (12 awg), exterior lighting circuit (12 awg), and one dedicated 20a circuit for a fridge (12 awg).
I'm also about 3/4 the way complete with grounding all of the main home outlets back to the interior sub panel. Just used green jacketed 12 awg solid for all of the grounding.
Here are my questions:
Am I missing anything above?
Is there anything I can do with the single phase 220v leg? Could I use it and the neutral to get 208v single phase to power a ductless mini HVAC system?
Is running 6/2 to the interior sub panel ok, or do I need 6/3? I hoping 6/2 is fine as I already have 125 ft of it.
Any other concerns or things to look out for in older home wiring?
Any help is greatly appreciated.
The house still has 3 phase run from the pole, even after I had the electric company change out the lines from the pole due to a bad neutral and unbalanced 120v legs. The wiring in the house was a nightmare, which I have slowly been chipping away at. Originally the mains from the meter ran into a wire gutter, where it was spliced and going to 3 panels and 2 disconnects. The house was wired with 12 awg copper with no ground. The original panel had been replaced with a 16 mini slot, main lug, GE panel. Who ever installed the panel ran it from an old 60A 3 phase disconnect box, with no high leg, and then ran 4 awg to power the panel. There were also 2 other sub panels installed on the side of the house, next to the gutter and meter, that have breakers for the pool, dryer, disposal/dishwasher, range, microwave, and an enclosed porch. There was also another old 3 phase disconnect that was powering the outside unit for the HVAC, that was wired off the 220v leg, 1 120v leg, and a neutral. Not sure why it was hooked up this way, but have since corrected it with 2 legs of 120v and a neutral. The best part is how the entire garage is run off of the kitchen lighting circuit, which is 12/2 with no ground that someone decided to put a 30a breaker on it.
I have since removed the splices in the electrical gutter, the 2 3 phase disconnects, 1 sub panel, and installed a 200a main panel next to the meter, and upgraded the wiring from the meter to the panel with #3 stranded copper. I left the 220v leg disconnect at the meter, as I don't any point to running 208v single phase to anything at the moment. The main panel currently has one old grounding rod installed and is also grounded to the cold water pipes.
So enough back ground, here is my current plan:
Everything will be moved into the 200a panel, which will feed the sub panel in the house off of a 60a breaker and another 60a sub panel to the garage.
A second copper grounding rod will be added to the main panel via 6 awg solid copper.
The wiring to the in home sub panel will be changed to 6/2 NM-B. From my understanding I will not need to run a separate ground to the in home sub panel, since the main panel is bonded and the sub panel is in the same structure.
The garage sub panel will be run with 3 x 6 awg stranded THHN and 1 x 10 awg stranded THHN for the ground. This will all be run in buried 1.25 conduit. The garage panel will not be bonded and will have its own 2 copper grounding rods on the separate bar for the grounds. The garage panel will have a 60a main disconnect (as well as the main panel), and will power 1 220v 30a plug (6 awg), 1 110v 30a plug (10 awg), interior lighting circuit (12 awg), interior outlet circuit (12 awg), exterior lighting circuit (12 awg), and one dedicated 20a circuit for a fridge (12 awg).
I'm also about 3/4 the way complete with grounding all of the main home outlets back to the interior sub panel. Just used green jacketed 12 awg solid for all of the grounding.
Here are my questions:
Am I missing anything above?
Is there anything I can do with the single phase 220v leg? Could I use it and the neutral to get 208v single phase to power a ductless mini HVAC system?
Is running 6/2 to the interior sub panel ok, or do I need 6/3? I hoping 6/2 is fine as I already have 125 ft of it.
Any other concerns or things to look out for in older home wiring?
Any help is greatly appreciated.