Upgrading home HVAC - do I need a bigger main panel?
musgofasta
Corona CA
1975 home with 100 amp main panel and original 3 ton packaged rooftop HVAC system. HVAC currently is on a 50 amp breaker.
My system needs replaced before summer heat and will need a 5 ton for the square footage added.
My HVAC friend doing the install said a 5 ton unit needs a 60 amp breaker and wouldn't be supported from a 100 amp panel and would need to move up to 200 amps.
Why couldn't (or shouldn't) I swap the 50 amp breaker for a 60 and run bigger wire to the HVAC unit?
This adds $2k to my HVAC install - not the end of the world but blows the budget!
going4speed
If you have all gas appliances a 100 amp might be okay. 100 amp is really marginal in today's power hungry society. If all your appliances like water heater, dryer, stove and range are electric then a 200 amp service should be considered. It may even be code in your area.
Stuff
A 60 amp breaker is fine in a 100 amp panel. The question is how much power does the unit draw? Check the "Minimum Circuit Ampacity" spec. Probably around 30 amps with your unit. Most likely you will be fine but you should get a load calc done to be sure. Might even be required as part of your addition.
zmaxmotorsports
South of omaha
:beer::beer::beer::beer::beer::beer::beer:
The newewr equipment usually draws a lot less amperage than the older stuff.;)
Pwrgeek
Texas USA
One thing you may run into is problems starting the compressor. A 100A panel would imply a 100A wire run from the utility (though some just run the same wire for anything smaller than 200 so you'd need to check). If it is smaller you may get a voltage flicker issue every time the compressor kicks on. If so you can try a larger starting capacitor but you may end up with a 200A panel no matter what you do. If it were me I'd get a cheap clamp on meter and put it on the panel and see what you pull with everything but the AC you're likely to use at the same time (oven, stove, hair dryer, and well pump was my magic combination). Then add the running amps for the new AC unit. If you get anything less than 80 you're good otherwise I see a new panel in your future.
bazar01
Leesburg, GA
A 5-ton Rheem RQPM packaged heat pump only needs 50A circuit with a 10kW back up heat strip. If gas heat, it will be way less than 50A.
As Zmax said, newer units have a lot less amperage draw.
musgofasta
Corona CA
I'm in So Cal so it will be gas heat and electric cooling. I'm will run check the amp draw on my current unit but I think I will be ok without a new panel.
At least until the second garage gets built !
DC73
Lubbock TX
Be sure and advise the power company that you are upgrading from a 3 ton to a 5 ton unit. Power companies don't always install service wire that matches the customers main size. They understand the panel rating is a max that is not likely to be seen and so they diversify the wire size down. Especially given the age of your home, it's quite likely the power company only has service wire of around 75 amps or so.
Voltage drop can become an issue with the larger AC unit. You may notice your lights dim or go out each time the compressor starts. If the power company tells you the existing service wire is sufficient for the load, ask them if it is sufficient for the voltage drop incurred when the new AC compressor kicks on.
Good luck,
DC
75gmck25
Alexandria, VA
Moving from a 3 ton to a 5 ton is a big step unless you have really added a lot of extra conditioned space. Have you had an HVAC contractor do a manual J calculation to verify that you need a unit that big?
If you go too big on the AC capacity it may short cycle on and off and you will not get the level of de-humidification you want. Newer AC units are more effective and more efficient, so going bigger is not always the best choice.
Bruce
Stuff
Also question if the supply and return ducts were increased to handle the additional airflow.