Hello. Breaker panel accepts 250mcm on feed-thru lugs but run requires 750mcm triplex aluminum wire.

What's the best way to adapt that size of conductor to those lugs?

I have found some ferrules that do just that but they are $120.00 each and would need 6 of them.

Is there any other way?
 
To avoid these ads, REGISTER NOW!

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,712
Location
East Bay SFO
You must be running a hell of a lot of amps or have a super long run or both.

That wire is good for what? 300 amps?
 
OP
C

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
You must be running a hell of a lot of amps or have a super long run or both.

That wire is good for what? 300 amps?

It's what is spec'd for 200 amps on a 350' run from the meter which will be 150' from transformer.

This **** gets expensive. I would rather do a primary extension but they won't use up the last remaining space in their junction box for a new transformer.

I would have to pay to extend the line to a new junction box, then from that box to a transformer on my property which then would also require giving them an easement which is more time, cost and headache. 😑
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,145
Location
Modesto, CA
what are you running on this line? highly doubt you will be running it at max....

if you step the wire down to 500KCMIL, you will be at 3.56% VD @ maximum load (200a)
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
A Polaris connector to get down to a smaller wire size for the connection.

Wow, looked up the pricing for that size and they may be what you already mentioned. $105 each




Could do a split bolt and the right tape. That'll be a ton cheaper but more work
 
Last edited:

OccupantRJ

Well-known member
Joined
May 15, 2009
Messages
11,384
Location
Eastern North Carolina
Assuming this for a shop? I have had a 200 amp panel in my previous shop on it’s own meter, and now I have more equipment in play on my current 60 amp supply in my shop, and do just fine.
milling machine
lathe
drill press
6x48 belt sander
bench grinder
two vertical bandsaws
2x48 belt sander
240 volt blast cabinet
120 volt blast cabinet
TV
parts washer
horizontal band saw
2.5 ton heat pump
etc, etc.
One man can only run so much at a time.
 
To avoid these ads, REGISTER NOW!

Dagny

Well-known member
Joined
Jul 25, 2014
Messages
3,043
Location
Northern Wi.
Quite often I will go with the wire that fits the lug. If there are large motors or electric heat your just gonna have to write a bigger check.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,726
Location
Long Island
A Polaris connector to get down to a smaller wire size for the connection.
Wow, looked up the pricing for that size and they may be what you already mentioned. $105 each
Could do a split bolt and the right tape. That'll be a ton cheaper but more work
Sure, but here's my question. What sort of panel has lugs that fit up to 250 MCM, that has enough space to handle 750 MCM and associated upsized conduit? And if you think $105 Polaris connectors are expensive, wait till you price out the upsized 1000A panel that has room for 750 MCM (not to mention the cost of breakers to fill it).
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,829
Location
NW Iowa
At that distance I would (and have) used 350. You will either splice it in a box next to the panel or use pin reducers if you have space.
 