URD to SER or URD all the way?

ArtisanFarms

Well-known member
Joined
Dec 24, 2020
Messages
98
Location
Phelps, NY
I’m going to have a 150 amp panel in my new shop.

To make the connection to my main panel I will have ~85’ run in the basement and ~ 75’ buried to the shop.

Does it make more sense to run URD the entire length and put it in conduit in the basement, or use SER in the basement and have a junction box at the outside wall to tie into the URD going to the shop?

Most of the run in the basement will be in a ~ 2’ x 2.5’ utility chase way with house wiring and plumbing.
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,593
Location
Fullerton, CA
URD is not flame resistant so you can't use it for inside wiring even in conduit.
SER cannot be buried.
Mobile Home Feeder cable can be used for both, but needs conduit for physical protection indoors.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
If it’s single rated URD, then it is not permitted for use inside the building.

use AL MHF entire length, must be in conduit indoors, or SER inside and transition to MHF for underground run
 
Last edited:

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,894
Location
Richmond, VA
The urd can't go inside your shop either, so you would have two transitions.

I wonder what use URD really serves with MHF available.
 